In reply to Art Michael's query re: Recognized Insulation Systems vs. just 
use of components rated that high individually.

I was told by UL several months ago that use of individually Recognized 
Components (wire, plastic, tape, etc) within their ratings is accepted when 
applying for Recognition of the Component they are used in (relays in my 
case) without being investigated as a Recognized Insulation System.

The catch is, however, a  Recognized Component containing a coil which was 
not qualified via a Recognized Insulation System is subject to acceptance or 
rejection IN THE END USE by determination of acceptability by the reviewer - 
while a coil based on an Insulation System must be accepted without question 
if used within it's Recognized rating.

This all means the same Recognized Component could be rejected in some 
applications and accepted in others based on the whim of the reviewer if the 
component was qualified without use of an R/C Ins. Sys..

My question to UL applied to single coil relays. Personally, I wonder if you 
would have that latitude in multi-winding devices where isolation is 
critical. Might be worth asking UL specifically before using it.

***** Comments are my own and do not represent views of the corporation 
*******

Harold Leipold
Senior Technical Specialist
Siemens Electromechanical Components Inc.
Tel. (812)386-2161
Fax. (812)386-2616
Internet    [email protected]


 ----------
From: Art Michael
To: emc-pstc
Subject: UL 1950/CSA 22.2 No. 950
List-Post: [email protected]
Date: Monday, September 30, 1996 11:25AM

Hello all,

A) What is this group's sense with respect to the need for a UL Recognized
Insulation System (UL 1446) in a transformer operating in excess of Class
A (65 Deg/C Rise) conditions, when the power supply wherein this
transformer resides is being submitted for evaluation in accordance with
NRTL marking considerations.  NOTE: (Class B or better rated materials
will be used for building the transformer -- They just will not be part of
a UL Recognized Insulation System).

B) My reading of the Harmonized UL/CSA standard, UL 1950 / CSA 22.2 No.
950, Third Edition, indicates that a component satisfying the relevant UL
_or_ CSA component standard, can be used to satisfy the requirements of
the harmonized standard.  This rationale is derived from Paragraph 2.2.2
and the Annex P2 section addressing paragraph 2.2.2.  Both UL 1446 and CSA
22.2 No. 0, General Requirements - CEC, Part 2 are referenced.  To my
knowledge, neither CSA (nor IEC 85) require the "systems" approach.

C) Have I interpreted this correctly?

ThanX, Art Michael

A.E. Michael, Dir. of Engineering
Product Safety Int'l
166 Congdon St. East,
Middletown CT 06457-8061 U.S.A.

Phone  :  (860) 344-1651
Fax    :  (860) 346-9066
Email  :  [email protected]
Website:  http://www.safetylink.com







Reply via email to