Hello all,

A) What is this group's sense with respect to the need for a UL Recognized
Insulation System (UL 1446) in a transformer operating in excess of Class
A (65 Deg/C Rise) conditions, when the power supply wherein this
transformer resides is being submitted for evaluation in accordance with
NRTL marking considerations.  NOTE: (Class B or better rated materials
will be used for building the transformer -- They just will not be part of
a UL Recognized Insulation System).

B) My reading of the Harmonized UL/CSA standard, UL 1950 / CSA 22.2 No. 
950, Third Edition, indicates that a component satisfying the relevant UL
_or_ CSA component standard, can be used to satisfy the requirements of
the harmonized standard.  This rationale is derived from Paragraph 2.2.2
and the Annex P2 section addressing paragraph 2.2.2.  Both UL 1446 and CSA
22.2 No. 0, General Requirements - CEC, Part 2 are referenced.  To my
knowledge, neither CSA (nor IEC 85) require the "systems" approach.

C) Have I interpreted this correctly?

ThanX, Art Michael

A.E. Michael, Dir. of Engineering
Product Safety Int'l
166 Congdon St. East, 
Middletown CT 06457-8061 U.S.A.

Phone  :  (860) 344-1651
Fax    :  (860) 346-9066
Email  :  [email protected]
Website:  http://www.safetylink.com





 

Reply via email to