Doug,

To answer your question of which is better:

The primary concern should have been the temperature of the windings 
to see if the insulation (between primary and secondary?) would have 
exceeded the allowable limits and thus possibly break down.

A (much lesser) secondary concern would have been the risk of a fire 
starting either in the transformer or in other components due to the 
heating of the transformer.

Glenn Lesmeister


-----Original Message-----
From:   dmck...@paragon-networks.com 
[SMTP:dmck...@paragon-networks.com]
Sent:   Tuesday, September 16, 1997 5:35 PM
To:     IEEE Product Safety Technical Committee -
Subject:        Re: EN 60950 and component heating

Hi Kevin,

I had a rather bad experience between UL and CSA in
the older days when there wasn't so much discussion
and agreement between them.  I had set up an MOU
between them with UL as the test location.

Went like this ...

Switching power supply.  Has a transformer.
Must do abnormals on it.  UL does the abnormals.
Temp probe on the *windings* of the transformer.

CSA said, "No way. Since the real concern is
           the PCB flaming from over temps
           from the transformer, we want the
           probes on the *bobbin*."

UL said, "No way. Since the real concern is
          what generates the heat, we want the
          the probes on the *windings*."

To this day, I can't say absolutely which way
is the better.

Guess I didn't help you much either.

Regards,  Doug


> From: Kevin Harris <harr...@dscltd.com>
> To: EMC-PSTC (E-mail) <emc-p...@ieee.org>
> Subject: EN 60950 and component heating
> Date: Monday, September 15, 1997 6:14 PM
>
> Hello All,
>
> In testing some product for excessive temperatures I have come up
> against the following problem. Consider a diode (part of a bridge
> rectifier circuit) and the PCB underneath the component. If one 
measures
> the temperature of the diode it does not come close to the 
specification
> for the part. However if we place a thermocouple on the pad where 
the
> diode is attached to the PCB and we consider that as a temperature
> measurement for the PCB material itself ,then the temperature 
obtained
> is above the board manufacturers spec of 110 C (when we take into
> account our maximum permissible ambient  temperature of 49 C). By 
the by
> all this is NOT operator accessible if that makes any difference.
>
> Questions.
>
> 1. Is this a valid temperature measurement for the PCB? I'm of two 
minds
> on this. It could said that I'm really measuring the diodes 
temperature
> and not the PCB. On the other hand the diode pad does touch the PCB 