Thanks Rich:  I suspect you're right. Isn't that mechanism exactly what the
tracking index tests are meant to address?  I thought that any UL-approved
wiring device like this would have a material that is designed to resist
tracking, hence my speculation that contamination might be involved.  

I guess there are a few more comments to be made here...

1. From what I know, the tracking index tests are horribly non-repeatable
and are therefore somewhat meaningless.

2. The standards for plug caps and for multi-taps may not refer to UL746 and
may not have any of their own requirements for tracking index of insulation.


3. We could take this as evidence that even compliance with the tracking
index requirements doesn't prevent carbonization of the material where
there's a high temperature heat source involved.

There are lots of people who unplug anything they are not actively using. I
guess it's not such a paranoid practice!

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com <http://www.xantrex.com> 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.




-----Original Message-----
From: Rich Nute [mailto:[email protected]]
Sent: Thursday, October 25, 2001 12:14 PM
To: [email protected]
Cc: [email protected]
Subject: Re: skinny power cords.





Hi Jim:


>   I'm curious:  given that North American plug blades are >1/2" apart,
there
>   must have been substantial contamination to aid in 120Vac jumping that
far
>   (arcing).  Did you identify any sort of contamination or moisture?

I don't believe contamination is a significant factor
in events such as this one.

I believe such events start with a loose connection
between the plug and the socket (or between the wire
and the socket parts).  A loose connection means 
that the contact area is relatively small.  In turn, 
this means high current density at the point of 
contact.  

The smaller the contact area, the greater the 
resistance of the contact.

The smaller the contact area, the greater the current 
density at the point of contact.

These two factors contribute to heating of the two
parts, the plug blade and the socket.  Heating tends
to reduce the "springiness" of the socket part, and
of the connection between the supply wire and the
socket (because they are thermally connected).

The heating also tends to degrade the surface of the
insulating material in which the conductors are mounted.

Heating also enhances oxidation of the plating on the
parts, which further increases the resistance of the
connections.

If the plug-connected appliance is "ON," arcing can
occur as the parts expand due to heating and make
various intermittant connections.  Arc temperatures
are very high, and can "burn" the surface of nearby 
insulating materials via radiation.

As the surface degrades, leakages occur across the
surfaces.  At this point, whether or not the appliance
is on or even connected is not a factor.  There is a
current path between the two poles along the surface
of the insulator.  This can either be between the 
socket parts, or between the wired parts.  The leakage
current causes further heating and micro-arcs where
the leakage path opens due to current density.  The
micro-arcs further damage the insulator until there
is nearly continuous micro-arcing.  I suggest this
is the source of the noise.  The heat from the micro-
arcing and the resistance of the carbonized surface 
of the insulator eventually lead to ignition and 
flames.

I admit that this is a hypothesis.  I believe that 
the process is more-or-less correct, but the details 
may not be correct.


Best regards,
Rich





-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to