I think the simple answer is no.  The NEC deals primarily with installation 
wiring and not with equipment plugged into that wiring.  A phrase similar to 
"where listed equipment is installed" is found in many sections of the code, 
generally where special installation conditions are acceptable which would not 
be generally accepted.  For instance, Article 645 deals with computer rooms.  
You are allowed to use the special provisions of the article if, among other 
things, 645-2(c) Listed information technology equipment is installed.

As a general rule, the NEC does require listed equipment within the building 
wiring such as receptacles, panelboards, etc.  But, the code does not require 
that all equipment have a safety agency listing.  It is an article by article 
issue.  A specific listing by UL is never required.  If listed equipment is 
required, the listing must be from a NRTL (Nationally Recognized Testing 
Laboratory).  A list of NRTL's may be found on the OSHA website.

At least as far back as 1982 some articles in the code required listed 
equipment.

The NEC is issued every three years.  It is not a regulation.  It only has the 
force of law when adopted by a legal jurisdiction -- town, city, county, state, 
etc.  And, even though the NEC is updated every three years, local legislation 
may not be.  There are some cities whose electrical code ordnance is the NEC 
from as far back as 2988 or earlier.
John P. Wagner
Regulatory Compliance & Mandatory Standards
AVAYA Strategic Standards.
1300 W. 120th Ave, Room B3-D16
Phone/Fax: (303) 538-4241
[email protected]





> ----------
> From:         [email protected][SMTP:[email protected]]
> Reply To:     [email protected]
> Sent:         Wednesday, March 20, 2002 8:57 AM
> To:   [email protected]
> Subject:      NEC Question
> 
> 
> Colleagues:
> 
> The question was asked if all products sold in the US, 
> specifically industrial products, that plugged into 
> the mains had to be UL Listed.  The answer was that 
> not necessarily UL Listed, but according to the NEC 
> they did have to be listed, labeled, certified, 
> classified, etc., by a 3rd party.  The answer went on 
> to say that this was only applicable if the locality 
> in which the product were to be used, and their AHJ, 
> adhered to the NEC and that not all areas of the 
> country adopted and adhered to the NEC.
> 
> 1.  Do you agree with the above responses?
> 
> 2.  How long has the NEC required products to be 
> listed, labeled, certified, classified, etc.?
> 
> Your comments and feedback would be appreciated.
> 
> Thanks in advance,
> 
> Steve Brody
> [email protected] 
> 
> 
> -------------------------------------------
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
> 
> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
> 
> To cancel your subscription, send mail to:
>      [email protected]
> with the single line:
>      unsubscribe emc-pstc
> 
> For help, send mail to the list administrators:
>      Ron Pickard:              [email protected]
>      Dave Heald:               [email protected]
> 
> For policy questions, send mail to:
>      Richard Nute:           [email protected]
>      Jim Bacher:             [email protected]
> 
> All emc-pstc postings are archived and searchable on the web at:
>     http://ieeepstc.mindcruiser.com/
>     Click on "browse" and then "emc-pstc mailing list"
> 

Reply via email to