Piotr,

You seem most concerned about EMC and functionality, but there is also 
safety to consider.

You say that the line may be up to 1 km long.  With such a distance it 
seems likely that the equipment you will be interfacing with could be in 
another equipotential zone, and possible on a different phase of the ac 
mains supply.  There is also the possibility of transients being induced 
on your data lines and perhaps even the possibility of power cross.

Of course, you may be able to excercise good control over the 
installation and so the problems I mentioned above (which are not 
intended to be an exclusive list) are all covered.  However, there are 
good engineering reasons why long lines are electrically isolated.

Regards,

Richard Hughes

Safety Answers Limited
www.safetyanswers.ltd.uk

Piotr wrote:

 >
 > Hello,
 >
 > I posted my question at sci.engr.electrical.compliance and was
 > suggested to
 > post it here.
 > So here it is.
 >
 > I'm trying to find if it is possible to do RS485 without optoisolation.
 > EN61000-6-2 and EN50130-4 needs interface to work with common mode
 > disturbance in 150kHz to 100MHz range of 10V (80% AM modulation) and
 > 150 Ohm
 > source impedance. This gives me 18V top signal level. I've read that
 > it is
 > good practice to add extra 6dB (measurements inaccuracy and element
 > distortions).
 > This way I have 36V.
 > I wont to communicate with 115kb/s (I plan to use IC-s with limited
 > slew-rate), so even high impedance common mode choke should make no
 > problem.
 > I assume up to 32 devices and up to 1km line.
 > I see two solutions:
 > Solution 1.
 > CM choke 2x2mH + 2.2nF capacitor at each line to ground. This reduces
 > 36V to
 > acceptable values but gives me 1.1nF differential mode.
 > Can this 1n1 be a problem ?
 > I can increase L and decrease C. But the higher L the lower its resonant
 > frequency and I'll have more problems with attenuating higher
 > frequencies.
 > Solution 2.
 > CM choke 3x5mH with no capacitors. RS485 with third wire connecting
 > grounds
 > of communicating devices. I've read somewhere that only 3 wire RS485
 > is the
 > right solution. In this third wire I can place 100 Ohm to avoid ground
 > difference currents. This solution seems to be very good. One coil senses
 > the CM voltage and subtracts it from signal lines. If it is a good
 > solution
 > and RS485 is popular than CM choke manufacturers should have a large
 > offer
 > with 3 coil chokes of several mH inductance but they don't. CM chokes
 > with 3
 > (and more) wires are widely offered but for higher frequencies. From
 > that I
 > think that I am doing somewhere a mistake. But where ?
 >
 > Connected with that subject is the question: Can I connect my circuit
 > ground
 > with Earth ground via 100 Ohm, and than directly connect circuit
 > grounds of
 > communicating devices with this third wire. May be the choke will be not
 > needed at all (probably if I reduce my needs from 36V to 18V).
 > My devices are powered from external 12V power supply selected by
 > installer
 > (not me).
 > I don't know where the problems can arise from in this situation ?
 >
 > Thanks in advance for any comments.
 >
 > Piotr Galka  [email protected]
 >
 >
 >
 >
 > -------------------------------------------
 > This message is from the IEEE EMC Society Product Safety
 > Technical Committee emc-pstc discussion list.
 >
 > Visit our web site at:  http://www.ieee-pses.org/
 >
 > To cancel your subscription, send mail to:
 >      [email protected]
 > with the single line:
 >      unsubscribe emc-pstc
 >
 > For help, send mail to the list administrators:
 >      Ron Pickard:              [email protected]
 >      Dave Heald:               [email protected]
 >
 > For policy questions, send mail to:
 >      Richard Nute:           [email protected]
 >      Jim Bacher:             [email protected]
 >
 > All emc-pstc postings are archived and searchable on the web at:
 >     http://www.ieeecommunities.org/emc-pstc
 >




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to