Hello David,

I have the same experience.
In 1996 I didn't know what is EMC, ESD, Surge ,...
When I used RS485 transceivers ESD protected up to
15kV I supposed I can't do anything more.
More than 100 installations worked with no problems,
but one was on the hill. Twice a year (spring and autumn)
we had problems.

Piotr


----- Original Message ----- 
From: "Garnier, David S (MED)" <[email protected]>
To: "'Piotr'" <[email protected]>
Cc: <[email protected]>
Sent: Friday, February 06, 2004 8:22 PM
Subject: RE: RS485 and CM choke


> Hello,
> 
> Here is something else to consider, electrical storms - lightning.
> 
> True store.  MR was having trouble with hospital sites that
> had remote operators consoles (that were remotely located
> from the MR room, like the next hospital building over.)  Every
> time an electrical storm would come and a nearby lightning
> strike would occur the console interface electronics would
> get fried (because of the lightning induced voltage differentials
> between buildings.)  The solution was an fiber optics interface.
> 
> dave garnier> 
> David Garnier
> e GE Medical Systems
> ___________________________________________
>         David S. Garnier
>         Senior Technician
>         Functional & CT Engineering
>         3000 N. Grandview Ave - M/S W-1250
>         Waukesha, Wi. 53188
>         Tel: 262.312.7246
>         Cel: 414.915.6529
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]]On Behalf Of Piotr
> Sent: Friday, February 06, 2004 12:13 PM
> To: EMC-PSTC
> Subject: Re: RS485 and CM choke
> 
> 
> 
> Michael,
> 
> I posted exactly the same text. The 1 km is there, but not at the
> beginning.
> An year ago I thought it is important. Now I think no (from EMC point
> of view). The tests are made not on the 1km cable, but on 1m cable.
> The problems made by 1 km are simulated with disturbances inserted
> in that 1m. So for me the disturbance levels (set in standards) are what
> I
> am
> analysing to be sure my device will pass them.
> I agree in real live it is difference if I have 100m and 1km.
> I plan to allow 1km but only in one building. As RS485 must be connected
> in one line it is possible to have 1km in one building.
> 
> Transformers.
> RS485 has the low frequency elements and even DC. You can use RS485
> transceivers to communicate using transformers (I think) but with some
> curry
> signal modulated with your data and not the standard UARTs in
> microprocessors.
> With enough big trafos (my speed is 115kb/s, and there can be 9 zeros or
> ones
> in serie) you can probably transmit standard RS485 data, but the problem
> begins
> when the frame is ended, there is (can be) DC (3V) on line, than next
> frame
> begins.
> I suppose the first byte in each frame will be corrupted because 0 on
> trafo
> output corresponds to +3V on input. -3 on input gives -6 on output.
> After
> some
> time the output becomes to be correct. It is if everything is close to
> each
> other.
> Then analyse 1km cable.
> 
> Using small trafos - you must detect slopes and not states - it becomes
> to
> be not
> RS485.
> 
> Regards
> 
> Piotr
> 
> ----- Original Message -----
> From: "Nagel, Michael" <[email protected]>
> To: "EMC-PSTC" <[email protected]>
> Sent: Friday, February 06, 2004 1:44 PM
> Subject: RE: RS485 and CM choke
> 
> 
> >
> > Pjotr,
> >
> > In your original post in sci.engr.electrical.compliance you talked of
> a
> > cable length of up to 1km. This is not negligible and should also be
> > mentioned here.
> >
> > You have to deal with burst, surge and potential differences (earth is
> > not the same potential everywhere) as well.
> >
> > When you are in control of both ends of the communication link, you
> > can decide on how you do it.
> >
> > Wanting to avoid the higher cost of optoisolation - did you think of
> > using transformers? I do not have to deal with RS-485 very often, so
> > I leave the maths up to you, but this is comparably cheap.
> >
> > DSL - transformers should be OK for this, maybe E1/T1.
> > Using the center tap for filtering gives you a good common mode
> rejection.
> >
> > I haven't seen this solution for RS-485 yet, but maybe there is
> someone
> > else who did ... On the other hand I see no reason why this should not
> > work but I am ready to learn if there is one ...
> >
> > Best regards,
> > Michael
> >
> >  Michael Nagel - Senior EMC Engineer
> >
> >  FORCE COMPUTERS GmbH              Lilienthalstrasse 15
> >  A Solectron Company                         D-85579
> Neubiberg/Muenchen -
> > Germany
> >  Tel: +49-89-60814-0                            Fax: +49-89-60814-376
> >
> >  e-mail: [email protected]            WWW:
> http://www.forcecomputers.com
> >
> >
> >
> >
> >
> > > -----Original Message-----
> > > From: Piotr [mailto:[email protected]]
> > > Sent: Friday, February 06, 2004 11:40 AM
> > > To: EMC-PSTC
> > > Subject: RS485 and CM choke
> > >
> > >
> > >
> > > Hello,
> > >
> > > I posted my question at sci.engr.electrical.compliance and
> > > was suggested to
> > > post it here.
> > > So here it is.
> > >
> > > I'm trying to find if it is possible to do RS485 without
> > > optoisolation.
> > > EN61000-6-2 and EN50130-4 needs interface to work with common mode
> > > disturbance in 150kHz to 100MHz range of 10V (80% AM
> > > modulation) and 150 Ohm
> > > source impedance. This gives me 18V top signal level. I've
> > > read that it is
> > > good practice to add extra 6dB (measurements inaccuracy and element
> > > distortions).
> > > This way I have 36V.
> > > I wont to communicate with 115kb/s (I plan to use IC-s with limited
> > > slew-rate), so even high impedance common mode choke should
> > > make no problem.
> > > I assume up to 32 devices and up to 1km line.
> > > I see two solutions:
> > > Solution 1.
> > > CM choke 2x2mH + 2.2nF capacitor at each line to ground. This
> > > reduces 36V to
> > > acceptable values but gives me 1.1nF differential mode.
> > > Can this 1n1 be a problem ?
> > > I can increase L and decrease C. But the higher L the lower
> > > its resonant
> > > frequency and I'll have more problems with attenuating higher
> > > frequencies.
> > > Solution 2.
> > > CM choke 3x5mH with no capacitors. RS485 with third wire
> > > connecting grounds
> > > of communicating devices. I've read somewhere that only 3
> > > wire RS485 is the
> > > right solution. In this third wire I can place 100 Ohm to avoid
> ground
> > > difference currents. This solution seems to be very good. One
> > > coil senses
> > > the CM voltage and subtracts it from signal lines. If it is a
> > > good solution
> > > and RS485 is popular than CM choke manufacturers should have
> > > a large offer
> > > with 3 coil chokes of several mH inductance but they don't.
> > > CM chokes with 3
> > > (and more) wires are widely offered but for higher
> > > frequencies. From that I
> > > think that I am doing somewhere a mistake. But where ?
> > >
> > > Connected with that subject is the question: Can I connect my
> > > circuit ground
> > > with Earth ground via 100 Ohm, and than directly connect
> > > circuit grounds of
> > > communicating devices with this third wire. May be the choke
> > > will be not
> > > needed at all (probably if I reduce my needs from 36V to 18V).
> > > My devices are powered from external 12V power supply
> > > selected by installer
> > > (not me).
> > > I don't know where the problems can arise from in this situation ?
> > >
> > > Thanks in advance for any comments.
> > >
> > > Piotr Galka  [email protected]
> > >
> > >
> > >
> > >
> > > -------------------------------------------
> > > This message is from the IEEE EMC Society Product Safety
> > > Technical Committee emc-pstc discussion list.
> > >
> > > Visit our web site at:  http://www.ieee-pses.org/
> > >
> > > To cancel your subscription, send mail to:
> > >      [email protected]
> > > with the single line:
> > >      unsubscribe emc-pstc
> > >
> > > For help, send mail to the list administrators:
> > >      Ron Pickard:              [email protected]
> > >      Dave Heald:               [email protected]
> > >
> > > For policy questions, send mail to:
> > >      Richard Nute:           [email protected]
> > >      Jim Bacher:             [email protected]
> > >
> > > All emc-pstc postings are archived and searchable on the web at:
> > >     http://www.ieeecommunities.org/emc-pstc
> > >
> >
> > -------------------------------------------
> > This message is from the IEEE EMC Society Product Safety
> > Technical Committee emc-pstc discussion list.
> >
> > Visit our web site at:  http://www.ieee-pses.org/
> >
> > To cancel your subscription, send mail to:
> >      [email protected]
> > with the single line:
> >      unsubscribe emc-pstc
> >
> > For help, send mail to the list administrators:
> >      Ron Pickard:              [email protected]
> >      Dave Heald:               [email protected]
> >
> > For policy questions, send mail to:
> >      Richard Nute:           [email protected]
> >      Jim Bacher:             [email protected]
> >
> > All emc-pstc postings are archived and searchable on the web at:
> >     http://www.ieeecommunities.org/emc-pstc
> >
> 
> 
> -------------------------------------------
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
> 
> Visit our web site at:  http://www.ieee-pses.org/
> 
> To cancel your subscription, send mail to:
>      [email protected]
> with the single line:
>      unsubscribe emc-pstc
> 
> For help, send mail to the list administrators:
>      Ron Pickard:              [email protected]
>      Dave Heald:               [email protected]
> 
> For policy questions, send mail to:
>      Richard Nute:           [email protected]
>      Jim Bacher:             [email protected]
> 
> All emc-pstc postings are archived and searchable on the web at:
>     http://www.ieeecommunities.org/emc-pstc
> 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to