Note that the code permits EPO switches to be implemented with an orderly shutdown process. The NFPA 50 (NEC) clause 685 is used. It requires extra process documentation and approval, but you can do such things as delay shutdown during software save routines, delay automatic shutdown to permit abort action, etc. It also can work against intentional mischief. These steps can become crucial with some high reliability systems and chemical process operations. Bob Johnson ITE Safety
[email protected] wrote: > You are referring to a Shunt Trip circuit breaker. These circuit breakers > have an additional mechanism that will trip the actuator. The shunt trip > mechanism is activated by a switch closure. It does not degrade the normal > trip mechanism or contacts of the circuit breaker. The shunt trip circuit > breakers are a preferred method for remotely triggering a circuit breaker. > It is much safer than shorting the phases. > > The red buttons are commonly known as Emergency Power Off (EPO) buttons and > they are required by many electrical codes for specified applications. > They are typically used where there are life safety issues. It allows you > to shut down all of the equipment in an area making it safe for emergency > responders. If you were a fireman, would you want to enter a room with > hazardous voltages and hazardous moving machinery? > > Many people hate the EPO buttons because they provide a single point of > failure. An accidental activation of the EPO can shut down your equipment, > which can be expensive for large manufacturing facilities or computer data > centers. In these cases, you want an EPO that is designed to be easy to > activate in an emergency and hard to activate by accident. Manufacturing > locations typically use a version that shuts down just one piece of > machinery, known as an Emergency Stop, or E-Stop button. These buttons > need to be located such that the operator can easily reach them, especially > if the operator becomes entangled in the machinery. > > Ted Eckert > American Power Conversion Corporation > > The items contained in this e-mail reflect the personal opinions of the > writer and are only provided for the assistance of the reader. The writer > is not speaking in an official capacity for APC nor representing APC's > official position on any matter. > > > > "Kunde, Brian" > <brian_kunde@leco > tc.com> To > Sent by: <[email protected]> > [email protected] cc > > Subject > 10/05/2006 02:46 RE: shorting the mains prohibited - > PM Help > > > > > > > > > > > Instead of shorting the AC Mains, have you considered using a breaker > with a trip coil? We used one in a product where as a safety measure, if > something bad happened, we wanted to cut power to the entire machine. > All we had to do is short out a set of contacts which powered up the > trip coil to trip the mains breaker and all power was shut down. > > Going a different way, in my shop class in High School there were these > boxes with big red buttons hanging from cords from the ceiling all over > the shop. If you pushed any one of the red buttons, the power to the > entire shop would go off shutting down all the machines. Someone said > that when you pushed the red buttons, that it shorted out the AC and > popped the breaker for the entire room. Is that really how that was > done? > > Yet another story from my past. I know an electrician who if he is > going to work on a receptacle, he just takes a piece of wire and shoves > it in the receptacle to deliberately pop the circuit breaker. He says it > is faster than switching the breakers off and on one at a time till you > find the right one. That can't be good for the breaker, right? > > The other Brian. > > -----Original Message----- > From: [email protected] [mailto:[email protected]] On Behalf Of Don Gies > Sent: Thursday, October 05, 2006 3:17 PM > To: [email protected]; [email protected] > Subject: RE: shorting the mains prohibited - Help > > Gregory, > > You should recommend thermal overtemp cutouts in each power lead (if AC > mains) that open upon overtemp rather than closing upon overtemp, with > reference to IEC 60950-1, Clause 4.3.7 (Heating elements in earthed > equipment). > > Shorting the mains is probably going to annoy someone, if not your > safety certification engineer. > > We once did have a small dc secondary heater circuit with an overtemp > device that closed upon overtemp. Doing so shorted out the dc supply, > thereby opening a 7 A fuse in front of the overtemp device. I don't > remember exactly the reason for this (maybe we couldn't find a > Recognized dc thermostat that opened), but the design was OK'ed by our > NRTL engineer. > > Regards, > > Don Gies, N.C.E > Senior Product Compliance Engineer > Lucent Technologies > Holmdel, NJ 07733 USA > > -----Original Message----- > From: Gregory H. McClure [mailto:[email protected]] > Sent: Thursday, October 05, 2006 12:25 PM > To: [email protected] > Subject: shorting the mains prohibited - Help > > Gentlemen, > > I need your collective memory. > > I have an engineer that wishes to design a protection mechanism to apply > a short circuit across the mains in order to open a protection device > upstream to stop an over-heating fault. The protection device would be > in the product, we are not talking about depending on the protection in > the service panel. I will not let them go there. > > I remember somewhere in the past that one of the standards, or perhaps a > country deviation, specifically forbid shorting the mains as a means of > protection but I cannot find it. I think it is from the era when we were > using IEC 380 or 435 and UL 478 but I am not sure. > > Can someone out there point me to the standard and clause? or perhaps > the deviation or an OSM decision? > > I am looking for all of the arguments against this practice I can pull > together because I do not feel it is sound. It is one thing to crowbar > the output of a power supply to protect an expensive logic board from a > power supply over-voltage failure. It is quite another to short the > mains input. > > Many thanks, > > Gregory H. McClure > Lexmark Product Safety > 859 232 3240 office > 859 232 6882 fax > > Confidentiality Notice: > This e-mail message, including any attachment, is for the sole use of > the intended recipient(s) and may contain confidential information. Any > unauthorized review, use, disclosure or distribution is strictly > prohibited. If you are not the intended recipient, please contact the > sender, by e-mail, and destroy all copies of the original message. > > - > ---------------------------------------------------------------- > This message is from the IEEE Product Safety Engineering Society > emc-pstc discussion list. Website: http://www.ieee-pses.org/ > > To post a message to the list, send your e-mail to [email protected] > > Instructions: http://listserv.ieee.org/request/user-guide.html > > List rules: http://www.ieee-pses.org/listrules.html > > For help, send mail to the list administrators: > > Scott Douglas [email protected] > Mike Cantwell [email protected] > > For policy questions, send mail to: > > Jim Bacher: [email protected] > David Heald: [email protected] > > All emc-pstc postings are archived and searchable on the web at: > > http://www.ieeecommunities.org/emc-pstc > > - > ---------------------------------------------------------------- > This message is from the IEEE Product Safety Engineering Society > emc-pstc discussion list. Website: http://www.ieee-pses.org/ > > To post a message to the list, send your e-mail to [email protected] > > Instructions: http://listserv.ieee.org/request/user-guide.html > > List rules: http://www.ieee-pses.org/listrules.html > > For help, send mail to the list administrators: > > Scott Douglas [email protected] > Mike Cantwell [email protected] > > For policy questions, send mail to: > > Jim Bacher: [email protected] > David Heald: [email protected] > > All emc-pstc postings are archived and searchable on the web at: > > http://www.ieeecommunities.org/emc-pstc > > - > ---------------------------------------------------------------- > This message is from the IEEE Product Safety Engineering Society > emc-pstc discussion list. Website: http://www.ieee-pses.org/ > > To post a message to the list, send your e-mail to [email protected] > > Instructions: http://listserv.ieee.org/request/user-guide.html > > List rules: http://www.ieee-pses.org/listrules.html > > For help, send mail to the list administrators: > > Scott Douglas [email protected] > Mike Cantwell [email protected] > > For policy questions, send mail to: > > Jim Bacher: [email protected] > David Heald: [email protected] > > All emc-pstc postings are archived and searchable on the web at: > > http://www.ieeecommunities.org/emc-pstc > > - > ---------------------------------------------------------------- > This message is from the IEEE Product Safety Engineering Society > emc-pstc discussion list. Website: http://www.ieee-pses.org/ > > To post a message to the list, send your e-mail to [email protected] > > Instructions: http://listserv.ieee.org/request/user-guide.html > > List rules: http://www.ieee-pses.org/listrules.html > > For help, send mail to the list administrators: > > Scott Douglas [email protected] > Mike Cantwell [email protected] > > For policy questions, send mail to: > > Jim Bacher: [email protected] > David Heald: [email protected] > > All emc-pstc postings are archived and searchable on the web at: > > http://www.ieeecommunities.org/emc-pstc > > > - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. Website: http://www.ieee-pses.org/ To post a message to the list, send your e-mail to [email protected] Instructions: http://listserv.ieee.org/request/user-guide.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas [email protected] Mike Cantwell [email protected] For policy questions, send mail to: Jim Bacher: [email protected] David Heald: [email protected] All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstc ______________________________________________________________________ This email has been scanned by the MessageLabs Email Security System. For more information please visit http://www.messagelabs.com/email ______________________________________________________________________