Brian,

You are correct regarding the interlocking device - it needs to be  
designed and rated for this function, and should incorporate 'direct- 
drive' or 'positive-drive' type contacts, but this is not a mandatory  
requirement.

The interlocking device is not required to have direct control of the  
power to the prime mover. This can be done, but is typically limited  
to very simple equipment. The interlocking *system* is what must have  
final control of power to the prime mover - in this case it sounds  
like you are talking about a pneumatic actuator of some kind. This  
could be achieved by using a valve in the main pneumatic supply and  
the control valve for the actuator to provide you with diverse and  
redundant control of the pneumatic power to the actuator. If it is an  
electric output, such as a motor starter, then control power to the  
controller outputs could be switched, and an additional contactor  
installed at the point of supply to the branch feeder to create a  
similar condition.

If you want to use a programmable controller as part of your safety  
system, it must meet the reliability requirements required based on  
the hazards presented by the equipment, so step 1 is a risk assessment.

Step two is to apply the relevant parts of IEC 61508 to the design so  
that you can be confident that you have achieved a high enough SIL  
(Safety Integrity Level) for the application. There are parts in this  
standard that relate to the design and the validation.

If your equipment is reasonably hazardous - meaning that you have  
some hazards that will result in severe injuries or possibly a  
fatality - you will almost certainly end up with a requirement for  
redundant controllers with sophisticated cross-checking. Typical  
safety PLC's that meet these requirements often have two or three  
processors internally for program control, validated function blocks  
for gate interlock inputs, and redundant I/O.

If you plan to market the product in the EU, check to see if it is  
included in Annex IV of the Machinery Directive. You can download a  
copy at http://tinyurl.com/y8b592, or read it on line at http:// 
tinyurl.com/2zxnjs.  If it is explicitly included in the Annex IV  
list, then you will need Notified Body involvement before you market  
it. If not, you will need to complete the 'internal production  
controls' requirements and keep a Technical File on hand. Don't  
forget that there will also be Low Voltage, EMC and possibly other  
directives to deal with as well.

If you want to discuss this more off-line I would be glad to chat  
with you at your convenience.

-- 
Doug Nix, A.Sc.T.
IEEE PSES
Kitchener-Waterloo Section, Ontario, Canada

[email protected]
mobile (519) 729-5704
fax (519) 653-1318

Find me LinkedIn at http://www.linkedin.com/in/dougnix

On Jul 20, 2007, at 9:29, Kunde, Brian wrote:

> I have limited experience working with industrial machines with moving
> parts so I would appreciate any help you can provide.
>
> To protect an operator from moving parts, my understanding is that I
> have to use an approved interlock device (in this case a switch)  
> and it
> has to directly control the device that makes the motion (pneumatic
> solenoid).
>
> But on a future project, we would like to have the interlock switch  
> talk
> to an FPGA (silicon) and have firmware and software controls the  
> motion
> device after many sensor checks are made. These "checks" are quite
> complex where many things have to be just right in the right sequence
> for the motion to occur. Engineering is saying that the sequence is  
> too
> complex to limit with a simple interlock switch system.
>
> Is it possible to use silicon chips, firmware, and software in such a
> circuit? Can such an approach be used and if so what is involved in
> qualifying it?
>
> Thanks,
> The Other Brian
>
> LECO Corporation Notice:  This communication may contain  
> confidential information intended for the named recipient(s) only.  
> If you received this by mistake, please destroy it and notify us of  
> the error.  Thank  you.
>
> -
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society
> emc-pstc discussion list.    Website:  http://www.ieee-pses.org/
>
> To post a message to the list, send your e-mail to [email protected]
>
> Instructions:  http://listserv.ieee.org/request/user-guide.html
>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
>
>      Scott Douglas           [email protected]
>      Mike Cantwell           [email protected]
>
> For policy questions, send mail to:
>
>      Jim Bacher:             [email protected]
>      David Heald:            [email protected]
>
> All emc-pstc postings are archived and searchable on the web at:
>
>     http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

Reply via email to