In message <[email protected]>, dated Fri, 23 Jan 2009, Grace Lin <[email protected]> writes:
>Are vertical and horizontal groundplanes required for measuring >disturbance voltages per Section 4.3 of CISPR 15? CISPR 15 doesn't >mention any groundplane while CISPR 22 does. My colleague concludes >that groundplanes are not required. Do you agree with the conclusion? There is a requirement in the last paragraph of 7.3, which is, in effect, a ground plane, and there is another in 8.2, and another in 8.9, and another in B.2. I think you have to look very carefully through the standard (and do a word-search if you have an electronic copy). -- OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk Things can always get better. But that's not the only option. John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected]> All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstc Graphics (in well-used formats), large files, etc. can be posted to that URL. Website: http://www.ieee-pses.org/ Instructions: http://listserv.ieee.org/request/user-guide.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <[email protected]> Mike Cantwell <[email protected]> For policy questions, send mail to: Jim Bacher: <[email protected]> David Heald: <[email protected]>