In message <[email protected]>, dated Mon, 6 
Apr 2009, Brian O'Connell <[email protected]> writes:

>When you refer to "mains circuits", does this mean the 'mains' power 
>that enters the building, or is the individual distribution 
>circuit/node being reference ?
>
>Do you mean that a fuse, for an indvidual appliance, is better for 
>protection from fire than a breaker ?

No, this is a very specific case, of 'power cross' on to thin data 
cables. If the data cable conductors are ground-referenced (PELV), the 
cable may overheat because the fault current is not sufficient to clear 
a fuse or over-current breaker, but is very unlikely to be insufficient 
to operate a GFCI or RCD.

If the data cable conductors are not ground referenced (SELV), then the 
'power cross' can remain undetected, probably until someone touches the 
SELV circuit.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Things can always get better. But that's not the only option.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to