Earthing the output of a power source is one way of preventing faults within
the source between mains to output from energizing the output. It quickly
overloads and opens the mains circuit.
Relying on an earthing for protection of a signal circuit which runs any
distance from the source to protect it from mains short is unwise. It is
unlikely to operate overcurrent protection and may cause fires. For example
typical cat 5 wire (24AWG) is 0.088 ohms/meter which means lengths approaching
100m would not operate branch circuit protection but simply overheat.
Isolation of signal circuits from mains must be done by insulation and
separation, even when worried about rodent damage and other misuse.
Expecting earthing to protect from mains shorts for any long light gauge wire
is a mistaken concept.

Bob Johnson
ITE Safety <http://www.itesafety.com> 

John Woodgate wrote: 

        In message <[email protected]>
<mailto:[email protected]> , dated
Fri, 27 Mar 2009, Joe Randolph <[email protected]>
<mailto:[email protected]>  writes: 
        
        

                A Class 2 supply is the most common type of supply that I have 
seen for POE
injection.  And yes, the output should be isolated from earth ground to comply
with IEEE 802.3af. 
                


        Can somebody explain to me why an isolated power supply is 'safer' than 
an
earthed one? I am particularly concerned that this applies to IT networks and
anything else that may run through, for example, roof voids and similar
spaces. Within one room, as for Class II consumer products, the techniques is
probably acceptable. 
        
        I know there are 'segregation' requirements, but cable runs can be 
disturbed
by non-electrical people during maintenance. The point is that cable damage
(by humans, rodents or building movements) can create a connection between
live mains and the 'SELV' circuit. Since the latter is not earthed, the fault
can persist indefinitely, until someone contacts the SELV circuit. The hazard
is great, the probability is low, and to me that results in a tick in the
'unacceptable risk' box. 
        
        We now have the concept of 'PELV', protected extra-low voltage, which 
has
reinforced insulation from mains voltage AND is earthed (preferably at one
point only, to avoid currents due to earth potential differences. I think that
all 'SELV' requirements must be re-examined to see if they should be changed
to 'PELV'. In hazard-based terms, there is no contest. SELV has two
safeguards, PELV has three. 
        


                Personally, I do not see any safety compliance problems with 
this
construction when used as intended (inside lines). 
                
                By the way, one problem that I *have* seen with this 
construction is
performance related.  Most of these POE injection power supplies are switching
converters, and the Y-caps used on the input for EMI suppression create a
voltage divider that places a very high 50/60 Hz common mode noise signal
(typically one half of the AC mains voltage) on the Ethernet outputs.  
                


        How can Y-caps do that? Y caps go from both mains poles to earth. 
        
        

                This means that an IP telephone powered by the POE injector 
will be riding
on the 50/60 Hz common mode noise.  The analog audio circuits in the IP phone,
such as the microphone for a hands-free mode, can be sensitive to this common
mode noise and produce audible hum.  
                
                Grounding the chassis of the POE injector fixes the problem, 
but most of
these devices are ungrounded.  
                


        Then they cannot possibly have Y-caps. 
        
        

                So, the IP telephone has to be designed with an extraordinary 
level of 50/60
Hz common mode immunity in order to avoid hum in the analog audio path. 
                


        It sounds as though people are making some fundamental error that shows 
up as
this problem. 
        

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to