Hi, Joe.

On 27 Mar 2009 at 0:59, Joe Randolph wrote:
> 
> On 3/26/2009, Peter Tarver wrote:
> 
> > What if the power supply is Class 2 Equipment?
> 
> Hi Pete:
> 
> A Class 2 supply is the most common type of supply that I
> have seen for POE injection. And yes, the output should be
> isolated from earth ground to comply with IEEE 802.3af.
> 
> Personally, I do not see any safety compliance problems with
> this construction when used as intended (inside lines).

I was specifically responding to [email protected] 
statement:

> 2) The power supply in the sourcing equipment are 
>    isolated per IEEE 802.3 (1500Vrms).

in the context of Class 2 Equipment type power supplies 
needing (typically) 3 kV isolation to the AC Mains.  This 
is indeed safe and presents no issues.  I simply wanted to 
make certain that no one mistakenly assumed 1.5 kV 
isolation was all that might ever be required.  Probably a 
knee-jerk reaction on my part, since [email protected] 
probably already knows this.

Keep in mind, also, that there're differences between a 
Class 2 power supply, in the NEC sense, and a Class 2 
Equipment power supply, in the 60950-1 sense.  Between your 
wording and Robert Johnson's post, I'm not sure which you 
meant, though that doesn't matter much.


Peter Tarver
[email protected]

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to