Many years ago I helped CSA write TIL I-35 which covers automotive
inverters.  We did the drawings that John Woodgate suggests, and we
analyzed shock hazard potential under normal conditions and with a
single fault in the inverter or in the load appliance.  We included
Class 1 and Class 2 products in our deliberations.  As it is nearly
universal, we assumed that the car's battery had one side grounded to
the car chassis.  The result was that there are several ways to make
such inverters safe.  

The easiest is to ground the inverter chassis and the inverter output
receptacle ground slot back to the DC negative, creating an
equipotential system including the car chassis, the inverter chassis,
and the chassis of all Class 1 load appliances.  If you do that, whether
or not the inverter provides isolation becomes moot.

The insulation/isolation approach was also allowed, whereby the inverter
would be tested to see how much leakage current could flow from the AC
output line or neutral  back to DC + or -, and if the answer was less
than a shock hazardous value, then the inverter isolation was deemed to
be adequate protection against shock hazard due to ground faults in the
load appliance.  The isolation in the inverter transformer and between
the inverters AC output circuits and the inverter chassis could be Basic
because faulting that insulation would only pose a hazard if another
simultaneous fault was present and we weren't going for double-fault
safety.  In this approach, the provision of an output ground slot, and
what it's connected to, become moot.

Another option allowed was to add ground fault protection to the AC
output in which case isolation and grounding become moot.  

The worst thing you can do is to provide no isolation or inadequate
isolation in the inverter and provide a ground slot on the output
receptacle that connects to nothing.

On small inverters, the provision of an external ground stud on the
chassis is useless because nobody will ever connect it to anything.
Ever.  On larger inverters meant for RV's (caravans), such a stud is
required by UL458.

There are many low cost automotive inverters on the market that do not
adequately address these considerations.

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
phone: (604) 422-2546
mobile: (604) 418-8472
e-mail: [email protected]
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: [email protected] [mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, March 18, 2009 11:27 AM
To: 'Haynes, Tim (SELEX GALILEO, UK)'
Cc: [email protected]
Subject: RE: Intersting question!!

> What is the isolation between the DC and AC circuits?

No safety isolation is necessary between
the automobile DC and the inverter output
AC.  Indeed, for most inverters, safety
isolation would make the inverter much
larger and more expensive.  

Inverters generate plus and minus high 
voltage steps with respect to the DC. 
The steps approximate the energy-time
content of a sinusoidal waveform.  Such 
circuits cannot have one AC pole 
connected to the DC common.  

The AC output socket should be an earthing
type.  The earthing terminal of the socket 
should be connected to the common pole of 
the car's DC.  This creates the equipotential
environment with respect to the metal of
the car.


Best regards,
Rich

  

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to