I got Klaus Stimpers document referred to earlier in this thread:  Thanks

What I learned:

The theory assumes that most damage is done by small local discharges
caused by a discontinuous conductive path  (imagine condensation drops or small 
wet particles)
 called scintillations.  These are micro sparks  (visible with the right 
equipment) that 
create local temperatures well above 1000 degrees, and contribute to a local 
burning
disintegration of the (carbon containing)  base material in areas of about 0.2 
mm.
Once enough areas have been affected a full continuous (carbon) leakage path is
created on the surface  that may lead to further damage. 
This is a more or less statistical process.

The size and frequency of these scintillations and affected areas seem 
dependent of
the voltage and total damage is therefore a time integration of voltage over 
the creepage path.

In my opinion this leads to the conclusion that an average voltage value should 
be choosen,
Instead of rms, to determine creepage path, but I may overlook certain aspects. 
Correct me where I am wrong.

Stimper states that leakage currents due to fully continuous conductive paths
 can be neglected, and only in the last phase of drying, sufficient 
discontinuities
exist for scintillation.
Alternating humidity conditions such as day/night rhythms, in relatively cold 
(need for condensation droplets)
designs are most liable to creepage problems

Gert

 


-----Original Message-----
From: John Woodgate [mailto:[email protected]] 
Sent: Tuesday, May 13, 2014 2:18 PM
To: [email protected]
Subject: Re: [PSES] Creepage and RMS

In message <[email protected]>,
dated Tue, 13 May 2014, "ce-test, qualified testing bv - Gert Gremmen" 
<[email protected]> writes:

>The point is that creepage distances are determined such as that within 
>the limits of pollution degrees 1-3 , no substantial leakage 
>current(eventually leading to breakdown of the
>insulation) develops. Yes the reaction starts immediately
>(salt/electrodes) but the deterioration takes time.
>
>Testing with carbon would lead to infinite creepage distances.

The document you cite admits the presence of conductive pollution

Pollution degree 3
Conductive pollution occurs or dry non-conductive pollution occurs which 
becomes conductive due to condensation which is to be expected.
–
Pollution degree 4
Continuous conductivity occurs due to conductive dust, rain or other wet 
conditions.

In the past, when commutator motors were widely used, carbon dust pollution was 
very common. Infinite creepage distances were not required.
>
>Apparently the relation between voltage and insulation deterioration 
>was derived very experimentally .... read here:

In Table 2J, the transient voltages are specified as peak. In Table 1 (of a 
different standard), the 'rated' [sic] impulse voltages are not specified as 
peak so, under IEC rules, are to be taken as RMS. This is confusing.
--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk Nondum ex 
silvis sumus John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to