The following is just my opinion. It may be based on one or more of the 
following: scientific fact, science fiction, pure fiction, rumors, supposition, 
tribal lore, unfounded guesses and random thoughts.

Long ago, the card edge connectors used in early computers were not 
manufactured to very tight tolerances. One common maintenance procedure on the 
Apple II was to shut the computer off, open the case, remove each card and 
reinsert it. This cleaned off the accumulation on the card edge connectors and 
would sometimes restore normal operation of the computer. Modern devices are 
made with tighter tolerances and this type of maintenance is much less commonly 
required. Modern automobiles are full of various connectors and they commonly 
work for 20 years without somebody having to disconnect and reconnect every 
connector for maintenance.

However, that was all about low power connectors. I would expect that things 
would be different for high power connectors. If there is any significant 
current flowing, any coating or oxidation on a contact surface would raise the 
resistance leading to heating. The heat will either burn off the contamination 
leading to a restored connection, or it will increase the resistance of the 
connection leading to a rapid failure of the connection. It would seem unlikely 
you could have some type of contamination causing imparted performance for 
extended periods of time in a high power connector.

I would recommend against cycling circuit breakers. The detents will wear down 
with repeated actuations. This can reduce the holding force leading to the 
breaker tripping at a lower limit than originally specified. Opening a breaker 
under load will result in arcing in the breaker which can degrade the contacts. 
High quality breakers should have good arc suppression mechanisms. Generally, 
manual operation of a breaker is fairly benign and shouldn't be a significant 
issue. That being said, GFCI, AFCI and RCD circuits with monthly test buttons 
should be tested monthly. The device is designed to handle a monthly test for 
decades without significant degradation.

My biggest concern in power circuits would be that repeated disconnection and 
reconnection could degrade the contact over time. Spring forces and detents 
could be weakened leading to a poor connection. If the connection is degraded 
until there is a small air gap, arcing could lead to heating and failure.

Commercial and industrial circuit breakers do require regular maintenance. 
Please note that the article linked below is from an electrical construction 
trade magazine. "Low voltage" means less than 1000 V. The test procedure 
recommended in the article calls for a high current source rated for at least 
1000 A, so it is safe to assume that this is for much larger breakers than most 
of us will see.
http://ecmweb.com/content/maintaining-low-voltage-power-circuit-breakers

It seems to me that regularly disconnecting and reconnecting high power 
circuits isn't generally necessary. If you would like to try it, I recommend 
that once a month, you unscrew and reinsert every light bulb in your house 
followed by unplugging and reconnecting each lamp and appliance.

Ted Eckert
Compliance Engineer
Microsoft Corporation
[email protected]<mailto:[email protected]>

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: Crane, Lauren [mailto:[email protected]]
Sent: Friday, May 23, 2014 12:50 PM
To: [email protected]
Subject: [PSES] "exercising" connections for health?

I am puzzling over a notion that it is prudent to exercise connectors in power 
circuits "every once in while" (e.g., disconnect and reconnect them). I suppose 
the underlying idea is to scrape the touching surfaces and potentially disrupt 
forming oxides or accumulated pollution.  I saw the other day an article 
suggesting circuit breakers should be cycled every so often (~ once a year) for 
possibly similar reasons.

Does anyone know of a code of electrical maintenance, or similar, that might 
support or refute this notion?

Regards,
Lauren Crane
KLA-Tencor

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)