As far as I know in North Carolina the NEC is adopted by version so the 2017 
version will not apply until specifically adopted.  NC usually waits a few 
years after the initial release for things to shake out before adopting the 
latest.  And I believe the local inspector in NC has authority to accept or 
require what he wants regardless of the NEC.

-Dave

From: Scott Douglas [mailto:[email protected]]
Sent: Tuesday, July 26, 2016 3:44 PM
To: [email protected]
Subject: Re: [PSES] NEC 2017


Not only do states adopt specific versions, they often adopt just parts of 
specific versions. And unless they put specific language in the adoption law to 
allow newer or older sections, they are usually bound by what exactly was 
adopted.

On Jul 26, 2016 12:28 PM, "Joe Randolph" 
<[email protected]<mailto:[email protected]>> wrote:
Hi Pete:

Here’s my experience with keeping track of upcoming changes in NFPA 70.

For the last two years I have been following the development of the 2017 
edition of NFPA 70 because of some changes that it makes to Article 840, 
“Premises Powered Broadband Equipment.”  In order to see the current draft of 
the 2017 edition and the committee comments, I had to join the NFPA for $175, 
but it was worth it to me because the changes in Article 840 directly affected 
a project I was working on.

While joining the NFPA allowed me to view the current draft on my computer 
screen, there was no way to download the document or even copy anything more 
than what is on the screen.

In summary, it *is* possible to see the draft version as it develops, but it 
requires some effort.  This may have changed recently because I believe the 
final draft has been officially voted on and adopted.

On a related note, I have found that when each state or jurisdiction adopts 
NPFA 70 into their local laws, the legislation often specifies a specific 
edition of NFPA 70.  For example, as of last year when I was looking at this, 
the state of Connecticut’s law still called out the 2005 edition of NFPA 70.   
This seems problematic for dealing with changes in the NEC over time.

I’m not sure what happens when a revised requirement appears in an edition of 
NFPA 70 that is newer than the edition called out by the laws of the local 
jurisdiction.  Two types of situation can occur:


1)      The new requirement is MORE restrictive than the version in the edition 
called out in the legislation

2)      The new requirement is LESS restrictive than the version in the edition 
called out in the legislation

Does anyone in this group know how that works?  My impression that the specific 
individual doing the inspection (the AHJ) has wide latitude to pick and choose 
from both editions, but this may be a mistaken impression.  It certainly would 
create a lot of uncertainly for a company that is trying to deploy a single 
product throughout the USA.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848<tel:781-721-2848> (USA)
[email protected]<mailto:[email protected]>
http://www.randolph-telecom.com

From: Pete Perkins 
[mailto:[email protected]<mailto:[email protected]>]
Sent: Tuesday, July 26, 2016 12:36 PM
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] NEC 2017

Doug, et al,

               If you were really interested you would be involved in the 
committee that revises the NEC every 3 years and have already read the 
pertinent changes in which you are interested.

               All of these changes are done in an open forum and the documents 
seem available; I don’t follow them, however.

:>)     br,      Pete

Peter E Perkins, PE
Principal Product Safety & Regulatory Affairs Consultant
PO Box 23427
Tigard, ORe  97281-3427

503/452-1201<tel:503%2F452-1201>

[email protected]<mailto:[email protected]>

From: Doug Powell [mailto:[email protected]]
Sent: Friday, July 22, 2016 3:13 PM
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] NEC 2017

Have we established that the 2017 edition actually has NRTL vs Listed?

I would like to hear some clause references since it is nearly 600 pages.

Thanks,  Doug


Douglas E Powell
Colorado USA
[email protected]<mailto:[email protected]>
http://www.linkedin.com/in/dougp01

On Fri, Jul 22, 2016 at 3:20 PM, Richard Nute 
<[email protected]<mailto:[email protected]>> wrote:


The NEC is a model standard and intended to be adopted by local and state AHJs. 
 In doing so, the AHJs often take exception to some requirements, and add some 
requirements.  In adopting the NEC, the AHJs must specify what “listing” means 
– what third-party certifiers are acceptable to the local or state AHJ.  The 
NEC has not mentioned or specified by name a third-party certifier.

AHJs accept third-party certifications according to their local or state rules. 
 A specific NRTL certification may or may not be currently acceptable.

Now that the 2017 NEC specifies NRTL, it will be interesting to see how the 
local and state AHJs accept specific NRTLs, or NRTLs by standards (as does 
OSHA), or blanket all NRTLs.  Note that AHJs have different objectives than 
OSHA, who runs the NRTL program.


Rich


-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
&LT;[email protected]<mailto:[email protected]>&GT;

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas &LT;[email protected]<mailto:[email protected]>&GT;
Mike Cantwell &LT;[email protected]<mailto:[email protected]>&GT;

For policy questions, send mail to:
Jim Bacher &LT;[email protected]<mailto:[email protected]>&GT;
David Heald &LT;[email protected]<mailto:[email protected]>&GT;



--

Douglas E Powell

[email protected]<mailto:[email protected]>
http://www.linkedin.com/in/dougp01
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
&LT;[email protected]<mailto:[email protected]>&GT;

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas &LT;[email protected]<mailto:[email protected]>&GT;
Mike Cantwell &LT;[email protected]<mailto:[email protected]>&GT;

For policy questions, send mail to:
Jim Bacher &LT;[email protected]<mailto:[email protected]>&GT;
David Heald &LT;[email protected]<mailto:[email protected]>&GT;
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to