Mr Perkins,

Aware of the article 725 changes and other code stuff that would track this?

Brian

From: Pete Perkins [mailto:[email protected]] 
Sent: Thursday, July 28, 2016 10:47 AM
To: [email protected]
Subject: Re: [PSES] NEC 2017

Mike, et al,

               Thanx for looking up the specific NEC updates for the new 
edition.  

               Having a 50V limit like the Euro LVD seems like a good 
harmonization effort.  

               However, within TC108 we’re identifying a number of issues for 
ELV power distribution to other equipment (e.g. POE or 100W USB, etc.) to be 
safely used.  There will be additional requirements for these schemes for them 
to be used safely and it will be part of the certification process under the 
standards.  

:>)     br,      Pete

Peter E Perkins, PE
Principal Product Safety & Regulatory Affairs Consultant
PO Box 23427
Tigard, ORe  97281-3427

503/452-1201

[email protected]

From: [email protected] [mailto:[email protected]] 
Sent: Tuesday, July 26, 2016 5:15 PM
To: Pete Perkins <[email protected]>
Cc: EMC-PSTC <[email protected]>
Subject: Re: [PSES] NEC 2017

Pete --

Thanks for the suggestion. I looked on the NFPA.org website at the NFPA 70 
draft dated 4-8-2016 and there is a new section 422.6: 
"422.6 Listing Required
All appliances operating at 50 volts or more shall be listed."

The definition for "Listed" in article 100 of NFPA 70 is complicated (too much 
to re-type here) but: 1) sounds like an NRTL; 2) does not specifically use the 
term NRTL.

The definition for "Appliance" in article 100 of NFPA 100 starts off: 
"Utilization equipment, generally other than industrial..." and gives a few 
examples that could be either household or commercial (e.g., washing machine, 
air conditioning units, food mixers, deep fryers). Hard to tell the intent of 
the changes here.

I'm guessing from the format that both "Listed" and "Appliance" definitions are 
being tweaked this time around, but have not checked this against the 2014 
version.

Mike Sherman
Graco Inc.

________________________________________
From: "Pete Perkins" <[email protected]>
To: "EMC-PSTC" <[email protected]>
Sent: Tuesday, July 26, 2016 11:35:43 AM
Subject: Re: [PSES] NEC 2017

Doug, et al,
 
               If you were really interested you would be involved in the 
committee that revises the NEC every 3 years and have already read the 
pertinent changes in which you are interested.  
 
               All of these changes are done in an open forum and the documents 
seem available; I don’t follow them, however.  
 
:>)     br,      Pete
 
Peter E Perkins, PE
Principal Product Safety & Regulatory Affairs Consultant
PO Box 23427
Tigard, ORe  97281-3427
 
503/452-1201
 
[email protected]
 
From: Doug Powell [mailto:[email protected]] 
Sent: Friday, July 22, 2016 3:13 PM
To: [email protected]
Subject: Re: [PSES] NEC 2017
 
Have we established that the 2017 edition actually has NRTL vs Listed?
 
I would like to hear some clause references since it is nearly 600 pages.
 
Thanks,  Doug
 
 
Douglas E Powell
Colorado USA
[email protected]
http://www.linkedin.com/in/dougp01
 
On Fri, Jul 22, 2016 at 3:20 PM, Richard Nute <[email protected]> wrote:
 
 
The NEC is a model standard and intended to be adopted by local and state AHJs. 
 In doing so, the AHJs often take exception to some requirements, and add some 
requirements.  In adopting the NEC, the AHJs must specify what “listing” means 
– what third-party certifiers are acceptable to the local or state AHJ.  The 
NEC has not mentioned or specified by name a third-party certifier.  
 
AHJs accept third-party certifications according to their local or state rules. 
 A specific NRTL certification may or may not be currently acceptable.  
 
Now that the 2017 NEC specifies NRTL, it will be interesting to see how the 
local and state AHJs accept specific NRTLs, or NRTLs by standards (as does 
OSHA), or blanket all NRTLs.  Note that AHJs have different objectives than 
OSHA, who runs the NRTL program.
 
 
Rich

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to