1. Yes.
 
2. 
Original statement is true only if the substation output is at MV or higher. If 
it is at LV, the location is strictly RCLI (residential, commercial and light 
industrial). 
 
a) In most countries in Europe, yes, but in France there are some separate 
industrial LV networks. You have to look at the location and decide whether 
there are likely to be broadcast radio or TV receivers within 30 m. If so, it's 
RCLI.
 
b) Yes.
 
There is no way to categorize. I know of a single dwelling house with its own 
LV transformer. They are not very rare in rural parts.
 
But please bear in mind that it's the *user* who decides where to use a product 
and the manufacturer has no control. Obviously, the most flexible solution is 
the most costly, Class B emissions and Class A immunity.
 
With best wishes DESIGN IT IN! OOO – Own Opinions Only
 <http://www.jmwa.demon.co.uk/> www.jmwa.demon.co.uk J M Woodgate and 
Associates Rayleigh England
 
Sylvae in aeternum manent.
 
From: Kortas, Jamison [mailto:jamison.kor...@ecolab.com] 
Sent: Wednesday, October 19, 2016 3:35 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Criteria for determining industrial vs. non-industrial for 
EMC testing purposes
 
Doug- Thanks very much for this.
 
Within this group, I often get responses before the initial email, so I missed 
this one the first time through. Two questions:
 
1.      Is it safe to say that the same definitions hold true for immunity as 
well?
2.      Would the following statements be true as well?
Original Statement: If a location is fed from its own substation and there are 
no dwellings supplied from that substation, it’s an industrial location, and 
therefore Class A.
a.      If a location is not fed from its own substation, but there are no 
dwellings supplied from that substation, it’s not an industrial location, and 
therefore Class B.
b.      If a location is fed from its own substation and there are dwellings 
supplied from that substation, it’s not an industrial location, and therefore 
Class B.
 
Without knowing the details of every installation, is there a relatively simple 
way of categorizing types of buildings that would be fed by its own substation, 
for example?
 
 
Thanks,
 
Jamison
 
From: Doug Nix [ <mailto:d...@ieee.org> mailto:d...@ieee.org] 
Sent: Tuesday, October 18, 2016 11:25 AM
To: Kortas, Jamison < <mailto:jamison.kor...@ecolab.com> 
jamison.kor...@ecolab.com>
Cc: IEEE EMC PSTC < <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] Criteria for determining industrial vs. non-industrial for 
EMC testing purposes
 
My understanding has always been based on the Class and Group designations in 
CISPR 11 / EN 55011 for ISM equipment (based on the 2009 edition):
 
5.3 Division into classes
Class A equipment is equipment suitable for use in all establishments other 
than domestic and
those directly connected to a low voltage power supply network which supplies 
buildings used
for domestic purposes.
 
Class A equipment shall meet class A limits.
Warning: Class A equipment is intended for use in an industrial environment. In 
the
documentation for the user, a statement shall be included drawing attention to 
the fact that
there may be potential difficulties in ensuring electromagnetic compatibility 
in other
environments, due to conducted as well as radiated disturbances.
Class B equipment is equipment suitable for use in domestic establishments and 
in
establishments directly connected to a low voltage power supply network which 
supplies
buildings used for domestic purposes.
Class B equipment shall meet class B limits.

The key in all of this is the source of power supply for the equipment. If the 
equipment is supplied from mains that are shared with domestic establishments, 
then it must meet Class B requirements IMO.
 
If the equipment is intended for industrial use, i.e., Class A, where the power 
supply from the mains is not shared with domestic establishments, then Class A 
performance is acceptable.
 
The deciding factor is the sharing of the supply with domestic establishments. 
If a location is fed from its own substation and there are no dwellings 
supplied from that substation, it’s an industrial location, and therefore Class 
A.
 
Doug Nix
 <mailto:d...@ieee.org> d...@ieee.org
+1 (519) 729-5704
 
On 18-Oct-16, at 08:44, Kortas, Jamison < <mailto:jamison.kor...@ecolab.com> 
jamison.kor...@ecolab.com> wrote:
 
Good Morning,
 
What do you use for criteria when reviewing the intended environment in which a 
device will be placed to determine if it is industrial or non-industrial? I 
have seen and read varying opinions on what criteria to use.
 
It ranges from a transformer isolated factory to the nature of the other 
products in the immediate vicinity (a mechanical room in a grocery store = 
industrial due to the equipment in its immediate environment).
 
I am familiar with some of the definitions in places, but am not so sure that 
those are what are typically followed in practice.
 
I appreciate any thoughts. 
 
Thank you.
 
 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to < 
<mailto:emc-p...@ieee.org> emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at:  
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ieee-2Dpses.org_emc-2Dpstc.html&d=DQMFaQ&c=clRTYxLjfWTYQkksq4Trqw&r=SuXR4v_cWDGps50Ob7OgG3eGvjdtolb5h84QBM8NxmY&m=1JyJN-HFlrusePu9Dz8HJ8gzDD7g4WfZDNXFvYhwGS8&s=kOzJuYj4K6VV6ZiI81-7jBnIR3cgUGEtpLadD2KGceI&e=>
 http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at  
<https://urldefense.proofpoint.com/v2/url?u=http-3A__product-2Dcompliance.oc.ieee.org_&d=DQMFaQ&c=clRTYxLjfWTYQkksq4Trqw&r=SuXR4v_cWDGps50Ob7OgG3eGvjdtolb5h84QBM8NxmY&m=1JyJN-HFlrusePu9Dz8HJ8gzDD7g4WfZDNXFvYhwGS8&s=7s5rYGdAK_pRi_YGJddDuB2ejopJ0d8SWRXC2b8L-TM&e=>
 http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website:   
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ieee-2Dpses.org_&d=DQMFaQ&c=clRTYxLjfWTYQkksq4Trqw&r=SuXR4v_cWDGps50Ob7OgG3eGvjdtolb5h84QBM8NxmY&m=1JyJN-HFlrusePu9Dz8HJ8gzDD7g4WfZDNXFvYhwGS8&s=KxoRKXS9Lg3ZNY9Jt_gS9K1nqGwnr0W2eiVzecq39fw&e=>
 http://www.ieee-pses.org/
Instructions:   
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ieee-2Dpses.org_list.html&d=DQMFaQ&c=clRTYxLjfWTYQkksq4Trqw&r=SuXR4v_cWDGps50Ob7OgG3eGvjdtolb5h84QBM8NxmY&m=1JyJN-HFlrusePu9Dz8HJ8gzDD7g4WfZDNXFvYhwGS8&s=FgIkKCXLzD7x4sQ9tjkSvh9VTUWU5KTEfgmV1c_d0VU&e=>
 http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules:   
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.ieee-2Dpses.org_listrules.html&d=DQMFaQ&c=clRTYxLjfWTYQkksq4Trqw&r=SuXR4v_cWDGps50Ob7OgG3eGvjdtolb5h84QBM8NxmY&m=1JyJN-HFlrusePu9Dz8HJ8gzDD7g4WfZDNXFvYhwGS8&s=do-HrFFV3B9JHYflFKKmSxg3R_A9oVH1dqxwEr9Ghmw&e=>
 http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas < <mailto:sdoug...@ieee.org> sdoug...@ieee.org>
Mike Cantwell < <mailto:mcantw...@ieee.org> mcantw...@ieee.org>
For policy questions, send mail to:
Jim Bacher < <mailto:j.bac...@ieee.org> j.bac...@ieee.org>
David Heald < <mailto:dhe...@gmail.com> dhe...@gmail.com>
 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org> >
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> > 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> > 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to