Thermal equilibrium is impossible.  Thermal change is an exponential, never 
achieving the end-point.  

 

The test is to determine that some part does not exceed its temperature rating. 
 Plotting the (exponential) curve shows whether the temperature in question is 
or is not going to exceed its rating.  (Curve-fitting would be nice, but 
impossible.)  As soon as this determination is made, the test can be concluded.

 

Defining thermal equilibrium as ±2°C (3.6°F) is not achievable as thermal 
change is an exponential.  And, it is tight.  For a small (low thermal mass) 
part, air currents will change the temperature beyond this limit.

 

The statement does not reflect knowledge of primitive thermodynamics.  

 

Best wishes for the New Year!

Rich

 

 

From: Doug Powell [mailto:doug...@gmail.com] 
Sent: Thursday, January 05, 2017 2:47 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Thermal equilibrium - 10% rule

 

All,

 

The following has always been confusing for me, 

 

For those tests that require the DUT to reach thermal equilibrium, thermal 
equilibrium is considered to be achieved if after three consecutive temperature 
measurements taken at intervals of 10% of the previously elapsed duration of 
the test but not less than 15 min, indicate no change in temperature greater 
than ±2°C (3.6°F).

 

The portion of text "taken at intervals of 10% of the previously elapsed 
duration of the test" has been around for some time and it exists in several 
safety standards, the "not less than 15 min" can be other values like 10 
minutes, 5 minutes, etc.  I believe the intent is to minimize the number of 
data points being recorded for extremely long thermal tests. The idea makes 
sense when I think back to the days of manual data logging.  Nowadays, with the 
advent of automated data logging, this point probably becomes moot.  Still, the 
phrase bugs me and I would like to understand how this might be interpreted.

 

First the "previously elapsed duration" could indicate either the duration of 
the entire test or the duration of the last logging interval.  

 

Second, over a long test 10% of the previous interval very quickly shortens the 
logging intervals to something ridiculously small.  For example, in three data 
points interval of 1440 minutes (24 hours) will be reduced to 144 minutes (2.4 
hours) and then 14.4 minutes, at which point the 15 minute minimum takes over.

 

I generally record at a much shorter intervals, even if for several days and 
check for equilibrium at a modulus of 15 minutes, as required.

 

 

 

​Thanks,  Doug

​

 

-- 

 

Douglas E Powell

doug...@gmail.com <mailto:doug...@gmail.com> 
http://www.linkedin.com/in/dougp01


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to