You are quite right, but I wonder how many products actually use High Breaking Capacity (HBC) fuses, rated at 1500 A or so.

John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk
Rayleigh, Essex UK

On 2017-11-12 03:37, Ted Eckert wrote:

I would like to attempt a response to question 2 regarding adequate breaking capacity.

Fuses should have an ampere interrupt capacity (AIC) rating. A more extensive discussion can be found on an application note from Bussmann Fuse at this link<http://www.cooperindustries.com/content/dam/public/bussmann/Electrical/Resources/solution-center/technical_library/BUS_Ele_Tech_Lib_Interrupting_Rating.pdf>. Finding this rating for a fuse is easy. Figuring out what the potential fault current in your circuit would be is not easy. It will depend on the impedances within your product, your products power connection, building wiring and the step-down transformer providing power to your circuit. The rating of the branch circuit breaker usually doesn’t matter as much as the circuit impedances. If there is a fault leading to a dead short, the circuit breaker will take a cycle or two before it opens. The current surge during that period can be significant. I’ve seen available fault currents in the kiloampere range in residential applications and 50 kA in some commercial application, all on 20 A circuits.

This is a problem in power supply design and the fuse is often placed after the common mode choke. The choke provides enough impedance to limit the rise time of the current under fault conditions. This give the fuse the chance to open before the current exceeds the fuse’s AIC rating.

Long ago, I was working on a power supply that failed testing. Under fault conditions, the fuse would open catastrophically. The fuse had an AIC rating of 50 A and the current was hitting over 100 A before the fuse opened. The metal filament would vaporize and then condense across the circuit board leaving a thin metalized plating. The solution was to use a higher impedance choke. The designer had used the same common mode choke that was used in other designs. However, this was a smaller power supply. It turned out that a higher impedance but lower current rated choke was available in the same footprint. The current rating was still sufficient for the design and the new common mode choke solved the problem. Its impedance was high enough to limit the rise time of the current. Under fault conditions, the rise time was slow enough to allow the fuse to open before the current exceed the 50 A limit.

It’s hard to make accurate assumptions about the impedance of the circuits into which your product will be connected. Assume the worst-case based on electrical construction methods, transformers and other factors for your customer’s installations. Then you can calculate the breaking capacity your fuse will need. If you fuse is after impedance in your own product’s design, the calculations are simplified.

You can run testing on your product, but that can be more difficult to do. If you happen to insert a fault at the current’s zero crossing, you may not see the same instantaneous fault current you would see if the short is applied at the peak of the waveform. If you are using a laboratory AC supply, you may find that it has a lower available fault current than a wall outlet. If you have a good high-frequency current meter, you can watch the fault current to see if it is getting close to the AIC rating of your fuse. As with any measurement at hazardous voltages and with these currents, care should be taken to ensure that the setup does not create a hazard for the laboratory staff.

Ted Eckert

Microsoft Corporation

The opinions expressed are my own and do not necessarily reflect those of my employer.




-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to