Hi Mick:

Annex Q  in 60950-1 shows that the authors were concerned about increased 
leakage current in MOVs that are subjected to multiple surges.  Perhaps the 
authors assumed that if the equipment passed the earth leakage test with new 
MOVs, allowing the MOVs to deteriorate by up to 10% after the Annex Q surges 
would be acceptable.  

Unfortunately, Annex Q does not help to define the term "adequate breaking 
capacity" as called for in clause 1.5.9.2 for fuses required in series with the 
MOV.  As Rich Nute has pointed out, a fuse that will open when the leakage 
current exceeds 0.5 mA cannot be expected to survive a 3 kA surge.

So, the purpose of the fuse does not appear to be directed at the 0.5 mA 
leakage current requirement.  Rather, I think the authors were trying to use 
the fuse to protect against the three conditions itemized in clause 1.5.9.2:

* Temporary overvoltages
* Thermal overload due to increased leakage current
* Burning and bursting of the MOV in the event of a short-circuit fault

The problem with this is that it takes very little leakage current to cause 
thermal overload of the MOV.  At 230 VRMS, and RMS leakage current of 100 mA 
would dissipate 23 Watts in the MOV.  A fuse that reliably opens at 100 mA will 
not survive a 3 kA surge.  

In general, MOVs subjected to thermal overload allow more leakage current as 
they heat up.  With a fixed voltage supply (such as 230 VRMS), this creates a 
positive-feedback condition of ever-increasing power dissipation that 
eventually drives the MOV to destruction.

So, perhaps the requirement for "adequate breaking capacity" was directed at 
trying to prevent burning and busting of the MOV, rather than excessive earth 
leakage current.  So far, it appears that the term "adequate breaking capacity" 
is not actually defined in 60950-1.  I suppose that the authors intended 
"adequate breaking capacity" to mean "adequate to prevent burning and bursting" 
of the MOV.  

I'm not sure that this is even possible if that same fuse has to survive a 3 kA 
combination wave surge.  However, it is possible that 60950-1 does not actually 
require the circuit to survive such surges.  Perhaps all that 60950-1 requires 
is that the MOV itself tolerates such surges with no more than 10% degradation. 
 It would then be left to the product designer to select a suitable fuse.  
Between the conflicting goals of preventing nuisance tripping of the fuse and 
preventing overheating of the MOV, I'm not sure that an ordinary fuse can be 
found that meets both goals.

This may be why 62368-1 seems to be steering us to using a thermal fuse that 
senses overheating of the MOV, rather than a fuse that responds only to current.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
[email protected]
http://www.randolph-telecom.com


-----Original Message-----
From: Mick Maytum [mailto:[email protected]] 
Sent: Sunday, November 12, 2017 3:55 AM
To: [email protected]
Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on 
AC mains ports?

For my sins I am currently editing a 40 page MOV application guide. As the 
guide was written by a Chinese expert I have the additional task of translating 
the Chinlish to English. However this forces understanding and I found the 
document contains many gems I did not appreciate. On degradation three areas 
are mentioned:

1.      Varistor voltage at 1mA has decreased by more than 10 % of the 
initial value.
2.      Surge limiting voltage at a specified impulse current has increased 
by more than 10 % of the initial value.
3.      Leakage current or watt-loss shows a steady increase.

Then the comment is made that generally if the Varistor voltage has decreased 
by 10 %, the limiting voltage will have only increased by 3 %. 
Thus the Annex Q limiting voltage change limit of 10 % would be better replaced 
by a Varistor voltage change.

On fuses I did some calculations and found an anti-surge fuse in the 4 A region 
was required to withstand the Annex Q MOV requirement of a 3 kA
8/20 surge. It should be remembered that most fuses will not interrupt an 8/20 
surge as the fuse link plasma carries on conducing the 8/20 impulse current. 
Ted makes the excellent point that in the equipment additional series 
impedances will exist that reduce the peak the peak surge current from an 
1.2/50-8/20 generator.
Tests are now appearing for thermally protected MOVs, which disconnect the MOV 
in the event of exceeding a pre-set body temperature limit. 
Thermal disconnect, rather than current disconnect, gets to the heart of the 
matter. But, as far as I'm aware, none of these tests apply a surge voltage to 
check for open thermal switch arc over.

Regards,

Mick Maytum
Safety and Telecom
Standards
[email protected]
https://ictsp-essays.info

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to