For my sins I am currently editing a 40 page MOV application guide. As the guide was written by a Chinese expert I have the additional task of translating the Chinlish to English. However this forces understanding and I found the document contains many gems I did not appreciate. On degradation three areas are mentioned:

1. Varistor voltage at 1mA has decreased by more than 10 % of the initial value. 2. Surge limiting voltage at a specified impulse current has increased by more than 10 % of the initial value.
3.      Leakage current or watt-loss shows a steady increase.

Then the comment is made that generally if the Varistor voltage has decreased by 10 %, the limiting voltage will have only increased by 3 %. Thus the Annex Q limiting voltage change limit of 10 % would be better replaced by a Varistor voltage change.

On fuses I did some calculations and found an anti-surge fuse in the 4 A region was required to withstand the Annex Q MOV requirement of a 3 kA 8/20 surge. It should be remembered that most fuses will not interrupt an 8/20 surge as the fuse link plasma carries on conducing the 8/20 impulse current. Ted makes the excellent point that in the equipment additional series impedances will exist that reduce the peak the peak surge current from an 1.2/50-8/20 generator. Tests are now appearing for thermally protected MOVs, which disconnect the MOV in the event of exceeding a pre-set body temperature limit. Thermal disconnect, rather than current disconnect, gets to the heart of the matter. But, as far as I'm aware, none of these tests apply a surge voltage to check for open thermal switch arc over.

Regards,

Mick Maytum
Safety and Telecom
Standards
[email protected]
https://ictsp-essays.info

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to