I'm afraid that's not so. The short-circuit current of a 20 A circuit is normally at least 500 A, maybe 1500 A.

John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk
Rayleigh, Essex UK

On 2017-11-18 03:49, Joe Randolph wrote:

Yes, that is a very good point.  I may have misinterpreted what the term “adequate breaking capacity” means.  If all it means is that the fuse must be able to safely break the short-circuit current, then a 20 Amp, 250 VRMS fuse would be fine for use on a 20 Amp, 240 VRMS circuit.

Of course, this would not provide much protection against overheating of the MOV unless the MOV failed at an effective resistance of less than 12 ohms.  Anything higher than that would just keep producing heat.

Joe Randolph

Telecom Design Consultant

Randolph Telecom, Inc.

781-721-2848 (USA)

[email protected] <mailto:[email protected]>

http://www.randolph-telecom.com

*From:*John Woodgate [mailto:[email protected]]
*Sent:* Friday, November 17, 2017 4:47 PM
*To:* Joe Randolph <[email protected]>; [email protected]
*Subject:* Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on AC mains ports?

I agree with this step-wise route to failure. But I wonder about the intended meaning of 'adequate breaking capacity'. In the context of the fuse standard IEC 60027 (multi-part), this means that the fuse must not shatter or arc-over with the largest fault current that can be applied to it. It's all about the fuse, not about what it is supposed to protect.

I believe TVSs (BIG diodes with integral heat sink) are much nicer devices to use than MOVs. They don't suffer from energetic disruption.

John Woodgate OOO-Own Opinions Only
J M Woodgate and Associateswww.woodjohn.uk <http://www.woodjohn.uk>
Rayleigh, Essex UK

On 2017-11-17 21:39, Joe Randolph wrote:

    I have not performed any actual testing, but I believe that the basic 
problem is that MOV leakage current increases slightly each time the MOV 
experiences a big surge.  So, in the early stages of this mechanism, the 
leakage current will increase step-wise each time the MOV experiences a big 
surge.

    In practice, these successive "big surges" could be spaced months or years 
apart.  Each successive surge will increase the leakage current, but if the current 
remains well below the level that causes significant self-heating of the MOV, the 
situation will remain stable.

    After some number of big surges (which could take years to accumulate), the 
leakage current will have increased enough that the self-heating process itself 
leads to higher leakage current.  This sets up a positive feedback loop that 
causes the MOV to go into thermal runaway and self-destruct.

    I'm not sure the thermal runaway could be described as an "avalanche," 
since the process might take considerable time to destroy the MOV, but the general 
direction of the failure gets establishes as soon as the positive feedback mechanism gets 
started.

    If it could be shown that any dissipation level less than 240 W cannot cause ignition 
of nearby materials, then a 1A fuse would appear to provide the "adequate breaking 
capacity" called for in 60950-1.

    Joe Randolph

    Telecom Design Consultant

    Randolph Telecom, Inc.

    781-721-2848 (USA)

    [email protected] <mailto:[email protected]>

    http://www.randolph-telecom.com

    -----Original Message-----

    From: Ralph McDiarmid [mailto:[email protected]]

    Sent: Friday, November 17, 2017 1:05 PM

    To:[email protected] <mailto:[email protected]>

    Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground 
on AC mains ports?

    I wonder if a 1A fuse would protect against MOV flameout just as well as a 
100mA, if these MOV fail as an avalanche.  (get hotter = more leakage) I've 
seen some standards use 240VA (assume 240W) as a power limit for protection 
against fire.  However, I wonder if a MOV could burn nicely at say 0.5A without 
further increase in current.

    Ralph McDiarmid

    Product Compliance

    Engineering

    Solar Business

    Schneider Electric

    -----Original Message-----

    From: Joe Randolph [mailto:[email protected]]

    Sent: Monday, November 13, 2017 7:56 PM

    To:[email protected] <mailto:[email protected]>

    Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground 
on AC mains ports?

    Hi Mick:

    Annex Q  in 60950-1 shows that the authors were concerned about increased 
leakage current in MOVs that are subjected to multiple surges.  Perhaps the 
authors assumed that if the equipment passed the earth leakage test with new 
MOVs, allowing the MOVs to deteriorate by up to 10% after the Annex Q surges 
would be acceptable.

    Unfortunately, Annex Q does not help to define the term "adequate breaking 
capacity" as called for in clause 1.5.9.2 for fuses required in series with the MOV. 
 As Rich Nute has pointed out, a fuse that will open when the leakage current exceeds 0.5 
mA cannot be expected to survive a 3 kA surge.

    So, the purpose of the fuse does not appear to be directed at the 0.5 mA 
leakage current requirement.  Rather, I think the authors were trying to use 
the fuse to protect against the three conditions itemized in clause 1.5.9.2:

    * Temporary overvoltages

    * Thermal overload due to increased leakage current

    * Burning and bursting of the MOV in the event of a short-circuit fault

    The problem with this is that it takes very little leakage current to cause 
thermal overload of the MOV.  At 230 VRMS, and RMS leakage current of 100 mA 
would dissipate 23 Watts in the MOV.  A fuse that reliably opens at 100 mA will 
not survive a 3 kA surge.

    In general, MOVs subjected to thermal overload allow more leakage current 
as they heat up.  With a fixed voltage supply (such as 230 VRMS), this creates 
a positive-feedback condition of ever-increasing power dissipation that 
eventually drives the MOV to destruction.

    So, perhaps the requirement for "adequate breaking capacity" was directed at trying to prevent burning 
and busting of the MOV, rather than excessive earth leakage current.  So far, it appears that the term "adequate 
breaking capacity" is not actually defined in 60950-1.  I suppose that the authors intended "adequate 
breaking capacity" to mean "adequate to prevent burning and bursting" of the MOV.

    I'm not sure that this is even possible if that same fuse has to survive a 
3 kA combination wave surge.  However, it is possible that 60950-1 does not 
actually require the circuit to survive such surges.  Perhaps all that 60950-1 
requires is that the MOV itself tolerates such surges with no more than 10% 
degradation.  It would then be left to the product designer to select a 
suitable fuse.  Between the conflicting goals of preventing nuisance tripping 
of the fuse and preventing overheating of the MOV, I'm not sure that an 
ordinary fuse can be found that meets both goals.

    This may be why 62368-1 seems to be steering us to using a thermal fuse 
that senses overheating of the MOV, rather than a fuse that responds only to 
current.

    Joe Randolph

    Telecom Design Consultant

    Randolph Telecom, Inc.

    781-721-2848 (USA)

    [email protected] <mailto:[email protected]>

    http://www.randolph-telecom.com

    -----Original Message-----

    From: Mick Maytum [mailto:[email protected]]

    Sent: Sunday, November 12, 2017 3:55 AM

    To:[email protected] <mailto:[email protected]>

    Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground 
on AC mains ports?

    For my sins I am currently editing a 40 page MOV application guide. As the 
guide was written by a Chinese expert I have the additional task of translating 
the Chinlish to English. However this forces understanding and I found the 
document contains many gems I did not appreciate. On degradation three areas 
are mentioned:

    1.       Varistor voltage at 1mA has decreased by more than 10 % of the

    initial value.

    2.       Surge limiting voltage at a specified impulse current has increased

    by more than 10 % of the initial value.

    3.       Leakage current or watt-loss shows a steady increase.

    Then the comment is made that generally if the Varistor voltage has 
decreased by 10 %, the limiting voltage will have only increased by 3 %.

    Thus the Annex Q limiting voltage change limit of 10 % would be better 
replaced by a Varistor voltage change.

    On fuses I did some calculations and found an anti-surge fuse in the 4 A 
region was required to withstand the Annex Q MOV requirement of a 3 kA

    8/20 surge. It should be remembered that most fuses will not interrupt an 
8/20 surge as the fuse link plasma carries on conducing the 8/20 impulse 
current. Ted makes the excellent point that in the equipment additional series 
impedances will exist that reduce the peak the peak surge current from an 
1.2/50-8/20 generator.

    Tests are now appearing for thermally protected MOVs, which disconnect the 
MOV in the event of exceeding a pre-set body temperature limit.

    Thermal disconnect, rather than current disconnect, gets to the heart of 
the matter. But, as far as I'm aware, none of these tests apply a surge voltage 
to check for open thermal switch arc over.

    Regards,

    Mick Maytum

    Safety and Telecom

    Standards

    [email protected] <mailto:[email protected]>

    https://ictsp-essays.info

    -

    ----------------------------------------------------------------

    This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to<[email protected]> 
<mailto:[email protected]>

    All emc-pstc postings are archived and searchable on the web at:

    http://www.ieee-pses.org/emc-pstc.html

    Attachments are not permitted but the IEEE PSES Online Communities site 
athttp://product-compliance.oc.ieee.org/  can be used for graphics (in 
well-used formats), large files, etc.

    Website:http://www.ieee-pses.org/

    Instructions:http://www.ieee-pses.org/list.html  (including how to 
unsubscribe) List rules:http://www.ieee-pses.org/listrules.html

    For help, send mail to the list administrators:

    Scott Douglas<[email protected]> <mailto:[email protected]>

    Mike Cantwell<[email protected]> <mailto:[email protected]>

    For policy questions, send mail to:

    Jim Bacher:<[email protected]> <mailto:[email protected]>

    David Heald:<[email protected]> <mailto:[email protected]>

    -

    ----------------------------------------------------------------

    This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to<[email protected]> 
<mailto:[email protected]>

    All emc-pstc postings are archived and searchable on the web at:

    http://www.ieee-pses.org/emc-pstc.html

    Attachments are not permitted but the IEEE PSES Online Communities site 
athttp://product-compliance.oc.ieee.org/  can be used for graphics (in 
well-used formats), large files, etc.

    Website:http://www.ieee-pses.org/

    Instructions:http://www.ieee-pses.org/list.html  (including how to 
unsubscribe) List rules:http://www.ieee-pses.org/listrules.html

    For help, send mail to the list administrators:

    Scott Douglas<[email protected]> <mailto:[email protected]>

    Mike Cantwell<[email protected]> <mailto:[email protected]>

    For policy questions, send mail to:

    Jim Bacher:<[email protected]> <mailto:[email protected]>

    David Heald:<[email protected]> <mailto:[email protected]>

    ______________________________________________________________________

    This email has been scanned by the Symantec Email Security.cloud service.

    ______________________________________________________________________

    -

    ----------------------------------------------------------------

    This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to<[email protected]> 
<mailto:[email protected]>

    All emc-pstc postings are archived and searchable on the web at:

    http://www.ieee-pses.org/emc-pstc.html

    Attachments are not permitted but the IEEE PSES Online Communities site 
athttp://product-compliance.oc.ieee.org/  can be used for graphics (in 
well-used formats), large files, etc.

    Website:http://www.ieee-pses.org/

    Instructions:http://www.ieee-pses.org/list.html  (including how to 
unsubscribe) List rules:http://www.ieee-pses.org/listrules.html

    For help, send mail to the list administrators:

    Scott Douglas<[email protected]> <mailto:[email protected]>

    Mike Cantwell<[email protected]> <mailto:[email protected]>

    For policy questions, send mail to:

    Jim Bacher:<[email protected]> <mailto:[email protected]>

    David Heald:<[email protected]> <mailto:[email protected]>

    -

    ----------------------------------------------------------------

    This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to<[email protected]> 
<mailto:[email protected]>

    All emc-pstc postings are archived and searchable on the web at:

    http://www.ieee-pses.org/emc-pstc.html

    Attachments are not permitted but the IEEE PSES Online Communities site 
athttp://product-compliance.oc.ieee.org/  can be used for graphics (in 
well-used formats), large files, etc.

    Website:http://www.ieee-pses.org/

    Instructions:http://www.ieee-pses.org/list.html  (including how to 
unsubscribe)

    List rules:http://www.ieee-pses.org/listrules.html

    For help, send mail to the list administrators:

    Scott Douglas<[email protected]> <mailto:[email protected]>

    Mike Cantwell<[email protected]> <mailto:[email protected]>

    For policy questions, send mail to:

    Jim Bacher:<[email protected]> <mailto:[email protected]>

    David Heald:<[email protected]> <mailto:[email protected]>



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to