Just a couple of points:

1. Inductive loads, like a relay coil, don’t have an inrush current, capacitors 
do.  Inductors need controlled de-energization (e.g. placing Zener across them 
or a snubber circuit)

2. Many SSRs do not switch correctly with high PF (large phase angle loads) 
like a.c. relay coils.  (i.e. where zero cross of voltage and current do not 
coincide)

We learned #2 the hard way when trying to switch in/out inductors in an LRC 
load bank using SSRs.  We ended up building a custom mosfet a.c. switch to open 
very close to zero cross on current  (and zero cross on voltage for capacitive 
elements)

Ralph McDiarmid
Product Compliance
Engineering
Solar Business
Schneider Electric


From: Peter Tarver [mailto:[email protected]] 
Sent: Friday, December 08, 2017 5:23 PM
To: [email protected]
Subject: Re: [PSES] Pilot rating

Hi, Jon.

Switching a contactor or relay coil does involve an inrush current and 
inductive kickback, as previously mentioned. This can affect air gap contacts 
in significant ways.

For solid state switching, I’m less familiar with the ins and outs, but if you 
look at some SSR manufacturers’ web sites, you can see that there are different 
P/Ns within a family of SSRs, depending on the nature of the switched load. For 
example, use

http://www.crydom.com/en/tools/parametric-search.shtml?type=panel

to go through some examples. 

Also, check out (not very detailed, but it gives a flavor)

http://www.eaton.com/ecm/idcplg?IdcService=GET_FILE&allowInterrupt=1&RevisionSelectionMethod=LatestReleased&noSaveAs=0&Rendition=Primary&dDocName=AP04901001E

There are bound to be some snubbing features built into these SSRs, just as 
there would be for an electromechanical relay.

A lot of SSRs are zero crossing types to prevent switching on higher voltages. 
This can prolong the life of the SSR.

It could simply be clever marketing to change a P/N, but it might also be that 
there’s a physical difference in the SSRs that make them better suited to 
certain types of loads.

It may be that your design satisfies all of the necessaries for piloting a 
contactor of a certain VA rating. An NRTL will likely want to do some testing 
to satisfy themselves that the special concerns are met by your design. If your 
company is not planning to sell the solid state switch, you can probably 
negotiate a reduced test program based on your application. If you do 
negotiate, make sure you build in some head room for load changes so you don’t 
have to repeat testing when someone gets a clever idea for how to repurpose 
your design.


Regards,

Peter Tarver

From: Richard Nute [mailto:[email protected]] 
Sent: Friday, December 08, 2017 13:09
To: mailto:[email protected]
Subject: Re: [PSES] Pilot rating


The ultimate issue is what safety issue occurs if the contactor fails to open 
or close when it is supposed to?  If there is no safety consequence, then the 
contactor control is functional, not a safeguard.  If there is a safety 
consequence, then the circuits controlling the contactor constitute a safeguard 
and must be “reliable,”  and must meet the intent of the standard.

Not so cynical Rich


From: Jon Keeble [mailto:[email protected]] 
Sent: Thursday, December 7, 2017 12:29 PM
To: mailto:[email protected]
Subject: [PSES] Pilot rating

I am using a Panasonic AQH3213A PhotoMOS optical isolator to control a small 
contactor.

At 110VAC the contactor coil draws 30mArms.
The coil contacts are wired to a PCB via a terminal block plug and socket.

On the PCB is a series 10ohm fusible resistor, and a SMBJ400AC bidirectional 
zener.

When the switch opens at peak current (42mA) there is 0.1J of energy in the 
coil that gets absorbed by the zener.

The zener 
* clamps at a voltage way below the voltage rating of the optoMOS switch.
* is rated at 600W for 8.3msec and is subject to only 13W for a similar period.

The UL test engineer says that the optoMOS should be "pilot duty" rated (the 
part I am using does have this rating).

Does anyone know what triggers the requirement for a "pilot duty" rating?
Is this defined in a standard somewhere?

This useful link identifies "contact rating codes"
https://na.industrial.panasonic.com/blog/what-pilot-duty-rating-how-it-obtained

The lowest rating E300 is for 110V 1.8A (make) 0.3A (break)

Technically speaking, my switch is not connected to the contactor .. there is a 
two-component network in between
Does UL have the capacity or procedures in place to understand and accept a 
circtuit analysis that shows my circuit as safe?

Jon Keeble

Wattwatchers.



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <mailto:[email protected]>
Mike Cantwell <mailto:[email protected]> 
For policy questions, send mail to:
Jim Bacher <mailto:[email protected]>
David Heald <mailto:[email protected]> 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <mailto:[email protected]>
Mike Cantwell <mailto:[email protected]> 
For policy questions, send mail to:
Jim Bacher <mailto:[email protected]>
David Heald <mailto:[email protected]> 

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <mailto:[email protected]>
Mike Cantwell <mailto:[email protected]> 
For policy questions, send mail to:
Jim Bacher <mailto:[email protected]>
David Heald <mailto:[email protected]> 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to