I think an example of the field inspection/label program not part of OSHA's 
NRTL program would be the City of Los Angles Department of Building and Safety.
http://www.ladbs.org/services/core-services/plan-check-permit/product-approval/electrical-test-lab

Note, I did not confirm they are not also an NRTL.

Respectfully,

Charles August-McDowell
Compliance Specialist

From: Regan Arndt <[email protected]>
Sent: Wednesday, February 19, 2020 10:46 AM
To: [email protected]
Subject: Re: [PSES] [EXTERNAL] Re: [PSES] Mandatory certification


[EXTERNAL EMAIL]
Hello Dave/Bernd.

Just a comment/clarification. The field inspection/label program is not part of 
OSHA's NRTL program despite some NRTL's that conducted this service. I know it 
can seem confusing but there are also some non-NRTL's that conduct these field 
evaluations, all of which are under state jurisdiction.

Some may think they are abiding by OSHA rules with obtaining a field evaluation 
by an NRTL. That is not the case.

Regan

On Wed, Feb 19, 2020 at 7:11 AM Nyffenegger, Dave 
<[email protected]<mailto:[email protected]>> wrote:
Bernd,

I don’t know any jurisdiction that would accept a manufacturer self-declaration 
if the jurisdiction is requiring a safety certification.  An alternative to an 
NRTL listing is an NRTL field inspection/label which is unique to each product 
at each  installation.

-Dave

From: Dürrer Bernd 
[mailto:[email protected]<mailto:[email protected]>]
Sent: Wednesday, February 19, 2020 10:02 AM
To: [email protected]<mailto:[email protected]>
Subject: [PSES] AW: [PSES] [EXTERNAL] Re: [PSES] Mandatory certification

Hello Ted, hello Regan,

Thank you for your clear statements on NRTL certification. Can you please 
provide some guidance on the interpretation of the National Electrical Code 
NFPA 70 (2020 edition), article 110.3, on the suitability of installation and 
use in conformity with the NEC? Informational note no. 2 explains, that this 
suitability “may” be evidenced by listing or labelling. Informative Annex A 
“provides a list of product safety standards used for product listing where 
that listing is required by the NEC.” This lists includes many product safety 
standards for consumer products like appliances that are typically plug 
connected. In the case that the NEC has been adopted by local jurisdiction and 
that the equipment is in the scope of a product safety standard listed in Annex 
A, is NRTL certification and listing then a mandatory requirement, or is there 
another option (e.g. self-declaration of the manufacturer that the product is 
suitable for installation and use in conformity with the NEC) that is accepted 
both by jurisdiction and the market?

Thank you and kind regards,

Bernd

Von: Regan Arndt <[email protected]<mailto:[email protected]>>
Gesendet: Dienstag, 18. Februar 2020 18:01
An: [email protected]<mailto:[email protected]>
Betreff: Re: [PSES] [EXTERNAL] Re: [PSES] Mandatory certification

OSHA & the related NRTL mandatory certification is only for the 
commercial/office/industrial workplace. OSHA has no jurisdiction in the 
consumer environment.
The FCC is for both environments.

Regan

On Mon, Feb 17, 2020, 8:29 PM 
<[email protected]<mailto:[email protected]>>
 wrote:
Thank you Ted, Rich and Regan,

The product is classified as IT and is sold to pro market. i.e it is used by 
professional and not consumer market. There two types of products. Class I as 
well as Class III. They are mainly used in corporation conference rooms.

With that in mind, what are your thoughts about mandatory NRTL certification as 
well as FCC?

Thanks
Peter
-----Original Message-----
From: Ted Eckert 
<[email protected]<mailto:[email protected]>>
To: EMC-PSTC <[email protected]<mailto:[email protected]>>
Sent: Mon, Feb 17, 2020 6:16 pm
Subject: Re: [PSES] [EXTERNAL] Re: [PSES] Mandatory certification
Hello Peter,

Let me add to Rich and Regan’s comments.

The question for residential installations isn’t as clear as for the workplace. 
Most jurisdictions in the United States have adopted the National Electrical 
Code which requires many electrical and electronic products to either be Listed 
or to be investigated and approved by the local Authority Having Jurisdiction. 
In practice, this typically will apply to hard-wired products or products 
attached to building structure. The enforcement is typically through an 
electrical inspection which will often not cover plug-connected devices.

In the workplace, any product that has a direct connection to the mains will 
need NRTL approval. At the other end of the spectrum, a product like a USB 
mouse or remote control using alkaline batteries likely won’t need NRTL 
approval. In theory, I believe an OSHA inspector could enforce the NRTL 
requirement on any electrical product, but that won’t necessarily be what 
happens in practice.

That being said, you can choose not to get NRTL approval for your product. 
However, you need to understand the risks your product may pose. If you sell 
products to commercial customers, are you meeting their needs? Will your 
products be acceptable to them? If you have a low-voltage device that isn’t 
mains connected, you will need to understand your customer’s needs before you 
make any determination about skipping NRTL approval.

Let’s use the USB mouse example. If you sell a USB mouse that has no NRTL 
approval, you can state that you are selling a product to the general public 
for home use where NRTL approval for a mouse is clearly not required. You can 
then argue that any business that purchases it is making their own decision on 
whether to accept a non-NRTL product. However, it is up to you, your employer 
and your employer’s legal department on whether you should take this approach.

Ted Eckert
The opinions expressed do not necessarily reflect those of my employer, OSHA or 
the U.S. Department of Labor.

From: Richard Nute <[email protected]<mailto:[email protected]>>
Sent: Monday, February 17, 2020 3:52 PM
To: [email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Re: [PSES] Mandatory certification


Hi Peter:

I can only speak to NRTL certification.

If your product can be used in a workplace, then NRTL certification is 
mandatory.

In most non-workplace locations, safety certification is mandatory.  A local 
authority specifies the acceptable certification houses.  Most local 
authorities specify the NRTL certification houses.

Certification by a NRTL certification house is accepted almost universally in 
the USA.

Best regards,
Rich


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C4ef9f645b43f44adca4a08d7b4046977%7C72f988bf86f141af91ab2d7cd011db47%7C0%7C0%7C637175803349145764&sdata=EdBJ6k%2FPdQeu60PsalDmtIEqa5PMzhzdo%2BkAhKJrtQE%3D&reserved=0>
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C4ef9f645b43f44adca4a08d7b4046977%7C72f988bf86f141af91ab2d7cd011db47%7C0%7C0%7C637175803349155760&sdata=dwSfp%2BU9BFjw5pnaQjhpPd8v8miHM0uP91TewlVEu08%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.
Website: 
http://www.ieee-pses.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C4ef9f645b43f44adca4a08d7b4046977%7C72f988bf86f141af91ab2d7cd011db47%7C0%7C0%7C637175803349165758&sdata=1iAcgn4unW1JsvYZj9dpknnUhBTaCn0269IMSsBK87I%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C4ef9f645b43f44adca4a08d7b4046977%7C72f988bf86f141af91ab2d7cd011db47%7C0%7C0%7C637175803349165758&sdata=S%2FKI2gIprmLZoaX7bynacercCoIJ5%2Bm1LID7VcDpKNs%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C4ef9f645b43f44adca4a08d7b4046977%7C72f988bf86f141af91ab2d7cd011db47%7C0%7C0%7C637175803349175751&sdata=xPNcGrhhjG0boDruvNyHVb2Sk%2BDJiPLqLGUIFfACE84%3D&reserved=0>
For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
&LT;[email protected]<mailto:[email protected]>&GT;

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas &LT;[email protected]<mailto:[email protected]>&GT;
Mike Cantwell &LT;[email protected]<mailto:[email protected]>&GT;

For policy questions, send mail to:
Jim Bacher &LT;[email protected]<mailto:[email protected]>&GT;
David Heald &LT;[email protected]<mailto:[email protected]>&GT;
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

________________________________


WILO SE
Nortkirchenstrasse 100, 44263 Dortmund
Amtsgericht Dortmund, HRB 21356
www.wilo.com<http://www.wilo.com>

Vorstand/Executive Board:
Oliver Hermes (President & CEO), Dr. Patrick Niehr, Georg Weber, Mathias Weyers
Aufsichtsratsvorsitzender/Chairman of the Supervisory Board:
Prof. Dr. Norbert Wieselhuber

Dieses Dokument ist vertraulich zu behandeln. Die Weitergabe sowie 
Vervielfaeltigung, Verwertung und Mitteilung seines Inhalts ist nur mit unserer 
ausdruecklichen Genehmigung gestattet. Alle Rechte vorbehalten, insbesondere 
fuer den Fall der Schutzrechtsanmeldung.
This document has to be treated confidentially. Its contents are not to be 
passed on, duplicated, exploited or disclosed without our expressed permission. 
All rights reserved, especially the right to apply for protective rights.

Datenschutz ist uns wichtig! Daher gehen wir sorgsam mit Ihren Daten um. 
Näheres finden Sie in unseren 
Datenschutzhinweisen<https://wilo.com/de/de/Wilo-Deutschland/Datenschutzhinweise.html>.
 Sollten Sie keinen Kontakt mehr mit uns wünschen, wenden Sie sich bitte an 
[email protected]<mailto:[email protected]>.
Data Protection is important to us! Therefore we handle your data carefully. 
Please find the details in our Note on Data 
Protection<https://wilo.com/de/de/Note-on-data-protection.html>. If you do not 
wish to stay in touch with us anymore, please write to 
[email protected]<mailto:[email protected]>.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
&LT;[email protected]<mailto:[email protected]>&GT;

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas &LT;[email protected]<mailto:[email protected]>&GT;
Mike Cantwell &LT;[email protected]<mailto:[email protected]>&GT;

For policy questions, send mail to:
Jim Bacher &LT;[email protected]<mailto:[email protected]>&GT;
David Heald &LT;[email protected]<mailto:[email protected]>&GT;
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

NOTICE: This email may contain confidential information. Please see 
https://meyersound.com/legal/#email-ms for our complete policy.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to