Igor Chudov wrote:
> Been reading the datasheet for the resolver: 11BRW-300-F10-10.pdf
>
>         http://igor.chudov.com/manuals/Harowe-Resolvers/11BRW-300-F10-10.pdf
>
> It calls for input voltage of 12 volts. I think that I give it much less
> than that, 4.7 volts or so.
>   
The resolver is a transformer, which varies the coupling with rotation.  
The AD2S1200 chip
MUST have approximately 3.6 V P-P when the resolver is turned to the 
maximum coupling
on that stator coil.  So, forget the rated input voltage on the 
resolver.  What you MUST do is
set the excitation level, with the jumpers, to satisfy the input signal 
requirement.

If the resolver has a 1:1 winding (12 V in, 12 V out) then 4.7 V input 
would be about right.

> Still trying to make sense of it, but I think I need more voltage on input.
>   
Set the OUTPUT to 3.6 V P-P at the peak angle of the resolver and see 
how it works.  That is the
procedure given by Analog Devices for their chip.