Kirk,

"Neutral" is not to be considered. You have two wires coming from the 
supplier. Adding a capacitor makes three of them. The two mains lines 
are 180  degrees apart by definition. The capacitor makes a third phase 
90 degrees between them. Connect your motor, and it will be running, 
regardless of which line is grounded.

Peter Blodow


Kirk Wallace schrieb:
> On Mon, 2011-03-14 at 17:58 +0100, Peter Blodow wrote:
> ... snip
>   
>> A capacitor connected to one leg of the two-phase system produces a 90 
>> degree phase shift relative to this lead. Using this as a mock three 
>> phase system, you will have 180 + 90 +90 degrees for a revolution 
>> including a direction information, depending to which leg you connected 
>> the capacitor. The distribution is uneven which is the reason for 
>> reduced power, but better than nothing. Don't confuse this with a 
>> starter capacitor used to supply a direction information to a generic 
>> two phase motor! Those are for short time use with small motors only and 
>> blow their tops when used continously (because of faulty starter relay 
>> or so).
>>     
>
> In case my attachment doesn't go through, here is my graphical study of
> a rotary three phase converter:
> http://www.wallacecompany.com/machine_shop/EMC2/three_phase_converter-1a.png 
>
> The 180 degree voltage phase shift is only an issue if neutral is used,
> but it is not. I think the decrease in efficiency is due to using one
> phase to try to generate two more and the currents are much higher than
> normal. (Viva VFD's)
>
>
>   


------------------------------------------------------------------------------
Colocation vs. Managed Hosting
A question and answer guide to determining the best fit
for your organization - today and in the future.
http://p.sf.net/sfu/internap-sfd2d
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to