Hi John,

You are correct I have a 220vac and a 120vac line coming into the 
machine. I didn't pull a 4 wire 220 line to those outlets in the shop so 
no neutral is there. If making a star ground doesn't fix the issue then 
I'll pull the 3 wire out and replace it with a 4 wire run. Not much fun 
but doable as I ran conduit up the wall to the attic.

Thanks for the great explanation, I'll save that and other things I've 
learned for future use.

JT

On 12/20/2015 2:25 PM, John Dammeyer wrote:
> Hi John,
>
> It sounds as if you have two AC lines coming into the machine.  One for the
> controller and one for the VFD.  The comments about a single star ground
> point are standard industry practice.  One breaker at the panel which
> protects the wire to the machine.  Another breaker inside the machine that
> protects the equipment.
>
> The Earth (green) comes in and is connected to a welded stud with a ring
> terminal, not a spade and double nutted so it can't possibly come loose.
> >From that point your controller and VFD are run.    Never ever rely on the
> frame to carry the AC Ground (Earth) from one section to another.
>
> DC grounds are isolated from Earth Ground.  You can, connect the DC power
> supply minus to the Earth ground and it may even be a code requirement where
> you are.  Be aware, some PCs do this inside their power supply as do other
> types of COTS hardware.
>
> And here is the problem you have to watch out for.  Just because your DC
> volt meter reads continuity  (Zero Ohms)  between all the ground points
> doesn't mean that there is actually a path of lowest resistance following
> what you think it should.
>
> The moment you get into the switching power world which includes the VFD,
> Stepper Motors and Servos along with switching power supplies you get
> something called impedance.  That's based on the DC resistance (usually low)
> and a combination of the wire inductance and capacitance and frequency.
>
> Depending on how things are wired and routed the impedance of the return
> signal of the VFD may be lower through the RS232 (RS485) shield than it is
> through the green wire or even the shield around the power cable.  So just
> imagine the very noisy VFD signal returns through the communication shield
> because that has an impedance of 200 Ohms while the green wire has 1K.
> That's problem #1.
>
> There's two types of electrical noise.  Electrical coupling and magnetic
> coupling.  Electrical you shield against.  Usually with the shield tied to a
> common earth somewhere.
> Magnetic coupling is the same thing that makes a transformer or a motor
> function.  A rapidly changing magnetic field caused by rapidly changing
> current in a wire is coupled onto another wire that is in close proximity.
> Shielding doesn't protect against that. Twisted pairs do to a certain
> extent.
>
> The best protection is distance.  That's why you don't run the VFD power or
> Servo power tightly tie wrapped to the encoder signal.
>
> Therefore put the AC power side for the VFD on one side of the cabinet and
> run the control signals as far away as possible.
>
> There are lots of books written on this subject and probably as many
> opinions on what to do.  Ground shield at both ends.  Ground at one end.
> Don't ground.   Twist the wires.  Don't twist the wires.
>
> Start with the Star Grounding.  Make sure there aren't any DC paths that are
> unexpected as explained earlier.   Then start looking at how the noisy
> signals might find their way back through alternate paths.  Filters,
> Ferrites are all useful to block the signals.  Always best to block at the
> source.
>
> John
>
>
>
>
>
>
>> -----Original Message-----
>> From: John Thornton [mailto:j...@gnipsel.com]
>> Sent: December-20-15 10:27 AM
>> To: Enhanced Machine Controller (EMC)
>> Subject: Re: [Emc-users] Grounding Issues
>>
>>
>> I have a line reactor for the VFD but I've never hooked it up.
>>
>> http://www.automationdirect.com/adc/Shopping/Catalog/Drives/AC_Drive
>> _%28VFD%29_Spare_Parts_-a-_Accessories/AC_Line_Reactors/LR-23P0-1PH
>>
>> Speaking of VFD's mine is grounded to the breaker panel and not in the
>> machine anywhere. When I check from the ground terminal to the panel I
>> get 0 ohms so I assume that the back of the VFD is grounded to the
>> ground lug on the VFD.
>>
>> JT
>
> ------------------------------------------------------------------------------
> _______________________________________________
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users


------------------------------------------------------------------------------