Except for underground rural power where every house has a pad mounted 
transformer due to the distance between houses (I love the distance).

I bonded the neutral to the ground at both panels in the shop/garage and 
the panel at the house. I have ground rods at the house and shop/garage. 
The panels are back to back in the shop/garage and both are connected to 
the ground rod just outside the shop/garage. I was told this is correct...

JT

On 12/26/2015 6:32 PM, John Kasunich wrote:
>
>
> The transformer is typically mounted on a pole and serves several houses.
> The neutral is connected to a ground rod at the base of the pole.  There
> are three wires from the pole to each house - L1, L2, and Neutral (no ground).
>
> Each house has a ground rod.  The neutral from the transformer, the
> house ground rod, a connection from the house cold water plumbing (if
> copper), the neutrals from all the receptacles, and the ground wires from
> all the receptacles are all tied together at a large bus bar in the main 
> panel.
>
> Other than the tie point in the main panel, neutral and ground are kept
> separated throughout the rest of the building, including through any sub-
> panels in garages, etc.
>
>
> John Kasunich
>


------------------------------------------------------------------------------