The VFD filter has no place to connect a neutral... only hots and ground.

On 12/27/2015 5:10 PM, Gene Heskett wrote:
> On Sunday 27 December 2015 17:07:15 John Thornton wrote:
>
>> I've built a bunch of automation machines for Briggs and Stratton and
>> they never pull a neutral only 3 240v hots and a ground. We always
>> have a control transformer for the 120v stuff... I have the same here
>> now.
> After an hours searching thru it, and its the 1996 issue, a 240 volt
> single phase line w/o a neutral is legal if it goes only to that machine
> AND the machine was designed for that power configuration, eg is
> designed to run on 240 for everything.
>
> IOW if it goes anyplace else in the building besides that machine, it has
> to have a neutral too.  And of coarse grounded is a given.
>
> So in your case, you can utilize a 240-120 stepdown that is NOT an
> autoformer.  And from whats been said, that is what you are doing.
>
> However, speaking as a C.E.T., not having the neutral so that the filters
> you are installing can ship their noise back up that separate circuit,
> effectively isolated from what is supposed to be a nice quiet ground,
> does seem like it would put a lot of the absorbed noises into the
> grounding system. And unless putting the filters in fixes it, making me
> just a worry wart, I believe this may be much of your noise problem.
>
> Since we've come 19 years into the future since my copy of the NEC was
> put to bed & sold, with more efficient (and more noise sensitive) ways
> to do things now, I'd expect that a current copy of the NEC would more
> than likely have some additions designed to head off problems like this.
>
> Unfortunately a current copy is now at or somewhat north of a 120 dollar
> bill.
>
>> On 12/27/2015 3:52 PM, Gene Heskett wrote:
>>> On Sunday 27 December 2015 16:17:20 John Thornton wrote:
>>>> well there is no neutral because it's a 240vac circuit only...
>>> The only reason there is not a neutral is that the wire was never
>>> pulled. And I am not sure that missing neutral is NEC kosher.  My
>>> copy is now 17 years old, so I think I'd check a newer one to be
>>> sure.  With it, you wouldn't need the stepdown and isolation tranny
>>> because you would then have a pair of 120 circuits available in the
>>> machine.  But those loads MUST return on the neutral, they cannot
>>> use the static ground.
>>>
>>>> On 12/27/2015 12:16 PM, Bruce Layne wrote:
>>>>> On 12/26/2015 06:51 PM, John Thornton wrote:
>>>>>> There is no neutral in the machine, only L1 L2 and GND. The
>>>>>> Neutral for the house is bonded to ground at the panels.
>>>>> Electrician's  Joke:
>>>>>
>>>>> Q: What's the difference between neutral and ground?
>>>>> A: About six inches.
>>>>>
>>>>> There's a very good reason the return current is carried on the
>>>>> neutral and the ground should not carry any current in normal
>>>>> circumstances, but we do need to understand that electrons don't
>>>>> care about our conventions.  They're just as happy returning via
>>>>> the ground wire.  They don't know that the green wire is off
>>>>> limits for all but emergency traffic.
>>>>>
>>>>> The concept of ground/neutral functional equivalence is also a
>>>>> real life saver for anyone who might otherwise consider standing
>>>>> barefoot on a basement floor while hot wiring any line powered AC
>>>>> circuit.
>>> Cheers, Gene Heskett
>> ----------------------------------------------------------------------
>> -------- _______________________________________________
>> Emc-users mailing list
>> Emc-users@lists.sourceforge.net
>> https://lists.sourceforge.net/lists/listinfo/emc-users
>
> Cheers, Gene Heskett


------------------------------------------------------------------------------
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to