On 09/12/2016 12:43 PM, Gene Heskett wrote:
> Greetings all;
>
> I see by the spec sheet that the allegro 667 gear sensor can sink up to
> 25 mills.
>
> But with 3 such sensors on the end of a long cable back to the breakout
> board, probably 7 foot by the time I get it routed, I am concerned with
> the potential for crosstalk noise in spite of putting a bypass capacitor
> on the encoder itself.
Just don't source any more current than you actually need.  
I have 3 of these on my spindle encoder, the cable is 
certainly more than 7 feet, and right next to a VFD-powered 
motor.  No problems so far.
I have the pull-ups at the sensor end, and they are 1 K 
Ohm.  I do have a .1 uF (or possibly 1 uF) cap across the 
power at the sensor end junction block, that is maybe 4" 
from the actual sensors.  I used 4-conductor shielded cable, 
with the shield as the ground return (I know, not best 
practice, but I didn't have 5-conductor shielded cable).

Jon

------------------------------------------------------------------------------
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to