On Thursday 30 November 2017 09:30:20 Peter C. Wallace wrote:

> On Thu, 30 Nov 2017, Gene Heskett wrote:
> > Date: Thu, 30 Nov 2017 09:16:16 -0500
> > From: Gene Heskett <[email protected]>
> > Reply-To: "Enhanced Machine Controller (EMC)"
> >     <[email protected]>
> > To: [email protected]
> > Subject: Re: [Emc-users] omron encoders
> >
> > On Thursday 30 November 2017 06:19:58 Les Newell wrote:
> >> Ok, I looked trough your previous posts. It appears that you are
> >> getting 7161.17 counts per spindle revolution. Your max frequency
> >> in that case is (7161.17 * 3000) / 60 = 358058.5Hz. 358kHz is well
> >> within the range of the 5i25.
> >>
> >> What is your encoder filter set to?
>
> OK so a 358 KHz count rate means 89 KHz on A and B or about
> 5.5 uS high/low time so we set the filter to one half of that: 2.75 uS
> This works out to a encoder sample frequency of say 5.5 MHz
> with the (15 count) encoder filter on.
>
> > False.  True and it all dies at about 400 spindle rpms.
>
> This could be because of the encoder samplerate/filter setting or your
> interface
>
I wasn't sampleing near fast enough. I'll put those figures in right now.
Done.  Thanks.

Cheers, Gene Heskett
-- 
"There are four boxes to be used in defense of liberty:
 soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)