A technical supporter of the vendor said that SR1690WBR - my server model -
contains a bridge between IPMB and PSMI.
But, he doesn't know the reason why BMC cannot recognize a power supply.
Thanks,
From: Hank Bruning [mailto:h...@jblade.com]
Sent: Thursday, September 22, 2011 9:31 AM
To: S. H. Lee; ipmitool-devel@lists.sourceforge.net
Cc: Zdenek Styblik
Subject: Re: [Ipmitool-devel] measuring the power consumption of a server
It may recognize the power supply but it does not mean there is an
electrical bridge between the IPMB bus and PSMI bus.
Check with your vendor that bridging between the two buses is supported.
On Wed, Sep 21, 2011 at 8:22 PM, S. H. Lee <smil...@korea.ac.kr> wrote:
Hi,
I've attempted some possible solutions.
- updating BMC firmware (ver.: 0.57)
- updating BIOS
- reinstall IPMItool (ver. 1.8.11)
By any chance, may I need additional hardware connector for power supply?
During BIOS&BMC firmware update, BMC didn't automatically detect any power
supply.
Thus, I manually checked 'yes' for 'SSI power supply'.
I also carried out a FRU/SDR package update.
After these tries, BMC still recognizes a power supply.
> -----Original Message-----
> From: Zdenek Styblik [mailto:zdenek.styb...@gmail.com]
> Sent: Thursday, September 22, 2011 4:41 AM
> To: S. H. Lee
> Cc: ipmitool-devel
> Subject: Re: [Ipmitool-devel] measuring the power consumption of a server
>
> On Wed, Sep 21, 2011 at 2:56 PM, S. H. Lee <smil...@korea.ac.kr> wrote:
> > Thanks for your comments,
> >
> > In the last mail, I said that I have a SV7-2186. It isn't the model I
> have.
> > My server is Intel SR1690WBR with a S5500WBV.
> > I've checked some manuals and mailing lists.
> >
> > The problem of my server is that IPMI cannot detect a power supply.
> >
> > BB +1.1V IOH | 1.084 | Volts | ok | na | 1.027
> > | 1.054 | 1.146 | 1.177 | na BB +1.1V P1 Vccp | 0.933
> > | Volts | ok | na | 0.683 | 0.708 | 1.501 |
> > 1.543 | na BB +1.5V P1 DDR3 | 1.505 | Volts | ok |
> na
> > | 1.362 | 1.401 | 1.589 | 1.635 | na BB +1.8V AUX
> > | 1.781 | Volts | ok | na | 1.673 | 1.720
> > | 1.874 | 1.927 | na BB +3.3V | 3.296 | Volts
> > | ok | na | 2.982 | 3.067 | 3.525 | 3.625 |
> > na BB +3.3V STBY | 3.239 | Volts | ok | na |
> > 2.982 | 3.067 | 3.525 | 3.625 | na BB +5.0V |
> > 4.971 | Volts | ok | na | 4.471 | 4.630 |
> > 5.380 | 5.538 | na BB +5.0V STBY | 4.886 | Volts
> > | ok | na | 4.416 | 4.565 | 5.272 | 5.421 |
> > na BB +12.0V | 12.039 | Volts | ok | na |
> > 10.739 | 11.103 | 12.923 | 13.287 | na BB +1.35v P1 MEM |
> > na | Volts | na | na | 1.236 | 1.271 |
> > 1.443 | 1.484 | na Baseboard Temp | 27.000 | degrees C
> > | ok | na | 5.000 | 10.000 | 61.000 | 66.000 |
> > na Front Panel Temp | 26.000 | degrees C | ok | na |
> > 0.000 | 5.000 | 44.000 | 48.000 | na IOH Therm Margin |
> > -44.000 | degrees C | ok | na | na | na |
> > 5.000 | 10.000 | na Mem P1 Thrm Mrgn | -36.000 | degrees C
> > | ok | na | na | na | 5.000 | 10.000 |
> > na Processor 1 Fan | 7616.000 | RPM | ok | na |
> > 640.000 | 768.000 | na | na | na Processor 1A Fan |
> > 5440.000 | RPM | ok | na | 640.000 | 768.000 |
> > na | na | na Memory Fan 1 | 5184.000 | RPM
> > | ok | na | 640.000 | 768.000 | na | na |
> > na Memory Fan 1R | 7616.000 | RPM | ok | na |
> > 640.000 | 768.000 | na | na | na Processor 2 Fan |
> > 7424.000 | RPM | ok | na | 640.000 | 768.000 |
> > na | na | na Processor 2A Fan | 5056.000 | RPM
> > | ok | na | 640.000 | 768.000 | na | na |
> > na Memory Fan 2 | 7616.000 | RPM | ok | na |
> > 640.000 | 768.000 | na | na | na Memory Fan 2R |
> > 5824.000 | RPM | ok | na | 640.000 | 768.000 |
> > na | na | na
> > P1 Therm Margin | -56.000 | degrees C | ok | na | na
> > | na | na | na | na
> > P1 Therm Ctrl % | 0.000 | unspecified | ok | na |
> na
> > | na | 11.700 | 19.500 | na Pwr Unit Status | 0x0
> > | discrete | 0x0000| na | na | na | na |
> > na | na IPMI Watchdog | 0x0 | discrete | 0x0000|
> na
> > | na | na | na | na | na Physical Scrty
> > | 0x0 | discrete | 0x0000| na | na | na
> > | na | na | na SMI Timeout | 0x0 | discrete
> > | 0x0000| na | na | na | na | na |
> > na System Event Log | 0x0 | discrete | 0x0000| na |
> na
> > | na | na | na | na System Event | 0x0
> > | discrete | 0x0000| na | na | na | na |
> > na | na
> > P1 Status | 0x0 | discrete | 0x8000| na | na
> > | na | na | na | na
> > P1 VRD Hot | 0x0 | discrete | 0x0000| na | na
> > | na | na | na | na CATERR | 0x0
> > | discrete | 0x0000| na | na | na | na |
> > na | na CPU Missing | 0x0 | discrete | 0x0000|
> na
> > | na | na | na | na | na IOH Therm Trip
> > | 0x0 | discrete | 0x0000| na | na | na
> > | na | na | na NM Capabilities | na | discrete
> > | na | na | na | na | na | na |
> > na
> >
> > As you can see above, 'Pwr Unit Status' is not available.
> >
> > Do I have to configure BMC?
> > After BMC firmware update, I didn't change any configuration of BMC.
> >
> > Thanks,
> >
>
> Please, keep the flow of the e-mail consistent as well as ipmitool-dev in
> the loop, because that way you might get more answers and avoid couple
> other things.
>
> Anyway, to your server. I don't have access to these, so it is hard to
say.
> Yes, one option is to update BMC firmware, which should not reset its
> settings(note: should not). I would check changelogs to see whether there
> were some updates related to Power Supply or IPMI stack or alike.
>
> I'm not sure if any extra configuration of BMC is required, but again I
> have no experience with these servers.
>
> I'll keep thinking about it, but I'm not sure what I could come up with.
> Hmm if you check BMC/SP web interface, can you see readings of sensors
> there? Can you see readings of power supply there?
>
> I'm sorry I was not much of help.
>
> Z.
>
> >
> >
> > -----Original Message-----
> > From: Zdenek Styblik [mailto:zdenek.styb...@gmail.com]
> > Sent: Wednesday, September 21, 2011 6:00 PM
> > To: S. H. Lee
> > Cc: ipmitool-devel@lists.sourceforge.net
> > Subject: Re: [Ipmitool-devel] measuring the power consumption of a
> > server
> >
> > On Tue, Sep 20, 2011 at 10:18 PM, S. H. Lee <smil...@korea.ac.kr> wrote:
> >> Hi,
> >>
> >> I have a SV7-2186 server with a S5500WBV motherboard and a Xeon
> processor.
> >> Its power supply is TDPS-600EB from DELTA.
> >>
> >> I am planning to develop a software checking the power consumption of
> >> a server.
> >>
> >> According to some documents, the power consumption can be checked
> >> through PSMI interface.
> >>
> >> Thus, I've tried to get the information by using ipmitool which can
> >> read FRU data from a power supply.
> >>
> >> But, the fru command of ipmitool on my server only shows the FRU data
> >> for a motherboard.
> >>
> >
> > Hello,
> >
> > what is # ipmitool sdr list; or # ipmitool sdr list all; telling you?
> > I have queried Sun/Oracle's
> > X4170 and X4270m2 and both are showing /SYS/VPS and PSx readings. From
> here I get the Nac Names and then I would query FRUs directly eg. #
> ipmitool sensor reading /SYS/VPS; and stuff this data into RRD.
> >
> > Text above is just an example for inspiration and doesn't have to
> necessarily work for you.
> >
> > Anyway, try 'sdr list' and you will see, or should see, what sensors you
> can query for readings.
> >
> > Best regards,
> > Zdenek
> >
> >>
> >>
> >> I want to know how to get the power consumption information of a
> >> server by using IPMItool.
> >>
> >>
> >>
> >> Waiting for your reply and guidance.
> >>
> >>
> >>
> >> Thanks.
> >>
> >
> >
> >
> >
----------------------------------------------------------------------------
--
All the data continuously generated in your IT infrastructure contains a
definitive record of customers, application performance, security
threats, fraudulent activity and more. Splunk takes this data and makes
sense of it. Business sense. IT sense. Common sense.
http://p.sf.net/sfu/splunk-d2dcopy1
_______________________________________________
Ipmitool-devel mailing list
Ipmitool-devel@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/ipmitool-devel
------------------------------------------------------------------------------
All the data continuously generated in your IT infrastructure contains a
definitive record of customers, application performance, security
threats, fraudulent activity and more. Splunk takes this data and makes
sense of it. Business sense. IT sense. Common sense.
http://p.sf.net/sfu/splunk-d2dcopy1
_______________________________________________
Ipmitool-devel mailing list
Ipmitool-devel@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/ipmitool-devel