I would verify that PSU.  I don't see a TDPS-600EB listed on Delta's website
and the closest thing to it is the TDPS-600CB which does not look like it
has the PSMI (four or five) wire connector.

>-----Original Message-----
>From: S. H. Lee [mailto:smil...@korea.ac.kr]
>Sent: Wednesday, September 21, 2011 6:00 PM
>To: 'Hank Bruning'
>Cc: ipmitool-devel@lists.sourceforge.net
>Subject: Re: [Ipmitool-devel] measuring the power consumption of a server
>
>A technical supporter of the vendor said that SR1690WBR - my server model -
>contains a bridge between IPMB and PSMI.
>
>But, he doesn't know the reason why BMC cannot recognize a power supply.
>
>
>
>Thanks,
>
>
>
>From: Hank Bruning [mailto:h...@jblade.com]
>Sent: Thursday, September 22, 2011 9:31 AM
>To: S. H. Lee; ipmitool-devel@lists.sourceforge.net
>Cc: Zdenek Styblik
>Subject: Re: [Ipmitool-devel] measuring the power consumption of a server
>
>
>
>It may recognize the power supply but it does not mean there is an
electrical
>bridge between the IPMB bus and PSMI bus.
>Check with your vendor that bridging between the two buses is supported.
>
>On Wed, Sep 21, 2011 at 8:22 PM, S. H. Lee <smil...@korea.ac.kr> wrote:
>
>Hi,
>
>I've attempted some possible solutions.
>- updating BMC firmware (ver.: 0.57)
>- updating BIOS
>- reinstall IPMItool (ver. 1.8.11)
>
>By any chance, may I need additional hardware connector for power supply?
>
>During BIOS&BMC firmware update, BMC didn't automatically detect any power
>supply.
>Thus, I manually checked 'yes' for 'SSI power supply'.
>I also carried out a FRU/SDR package  update.
>
>After these tries, BMC still recognizes a power supply.
>
>
>> -----Original Message-----
>> From: Zdenek Styblik [mailto:zdenek.styb...@gmail.com]
>> Sent: Thursday, September 22, 2011 4:41 AM
>> To: S. H. Lee
>> Cc: ipmitool-devel
>> Subject: Re: [Ipmitool-devel] measuring the power consumption of a
>> server
>>
>> On Wed, Sep 21, 2011 at 2:56 PM, S. H. Lee <smil...@korea.ac.kr> wrote:
>> > Thanks for your comments,
>> >
>> > In the last mail, I said that I have a SV7-2186. It isn't the model
>> > I
>> have.
>> > My server is Intel SR1690WBR with a S5500WBV.
>> > I've checked some manuals and mailing lists.
>> >
>> > The problem of my server is that IPMI cannot detect a power supply.
>> >
>> > BB +1.1V IOH     | 1.084      | Volts      | ok    | na        | 1.027
>> > | 1.054     | 1.146     | 1.177     | na BB +1.1V P1 Vccp | 0.933
>> > | Volts      | ok    | na        | 0.683     | 0.708     | 1.501     |
>> > 1.543     | na BB +1.5V P1 DDR3 | 1.505      | Volts      | ok    |
>> na
>> > | 1.362     | 1.401     | 1.589     | 1.635     | na BB +1.8V AUX
>> > | 1.781      | Volts      | ok    | na        | 1.673     | 1.720
>> > | 1.874     | 1.927     | na BB +3.3V         | 3.296      | Volts
>> > | ok    | na        | 2.982     | 3.067     | 3.525     | 3.625     |
>> > na BB +3.3V STBY    | 3.239      | Volts      | ok    | na        |
>> > 2.982     | 3.067     | 3.525     | 3.625     | na BB +5.0V         |
>> > 4.971      | Volts      | ok    | na        | 4.471     | 4.630     |
>> > 5.380     | 5.538     | na BB +5.0V STBY    | 4.886      | Volts
>> > | ok    | na        | 4.416     | 4.565     | 5.272     | 5.421     |
>> > na BB +12.0V        | 12.039     | Volts      | ok    | na        |
>> > 10.739    | 11.103    | 12.923    | 13.287    | na BB +1.35v P1 MEM |
>> > na         | Volts      | na    | na        | 1.236     | 1.271     |
>> > 1.443     | 1.484     | na Baseboard Temp   | 27.000     | degrees C
>> > | ok    | na        | 5.000     | 10.000    | 61.000    | 66.000    |
>> > na Front Panel Temp | 26.000     | degrees C  | ok    | na        |
>> > 0.000     | 5.000     | 44.000    | 48.000    | na IOH Therm Margin |
>> > -44.000    | degrees C  | ok    | na        | na        | na        |
>> > 5.000     | 10.000    | na Mem P1 Thrm Mrgn | -36.000    | degrees C
>> > | ok    | na        | na        | na        | 5.000     | 10.000    |
>> > na Processor 1 Fan  | 7616.000   | RPM        | ok    | na        |
>> > 640.000   | 768.000   | na        | na        | na Processor 1A Fan |
>> > 5440.000   | RPM        | ok    | na        | 640.000   | 768.000   |
>> > na        | na        | na Memory Fan 1     | 5184.000   | RPM
>> > | ok    | na        | 640.000   | 768.000   | na        | na        |
>> > na Memory Fan 1R    | 7616.000   | RPM        | ok    | na        |
>> > 640.000   | 768.000   | na        | na        | na Processor 2 Fan  |
>> > 7424.000   | RPM        | ok    | na        | 640.000   | 768.000   |
>> > na        | na        | na Processor 2A Fan | 5056.000   | RPM
>> > | ok    | na        | 640.000   | 768.000   | na        | na        |
>> > na Memory Fan 2     | 7616.000   | RPM        | ok    | na        |
>> > 640.000   | 768.000   | na        | na        | na Memory Fan 2R    |
>> > 5824.000   | RPM        | ok    | na        | 640.000   | 768.000   |
>> > na        | na        | na
>> > P1 Therm Margin  | -56.000    | degrees C  | ok    | na        | na
>> > | na        | na        | na        | na
>> > P1 Therm Ctrl %  | 0.000      | unspecified | ok    | na        |
>> na
>> > | na        | 11.700    | 19.500    | na Pwr Unit Status  | 0x0
>> > | discrete   | 0x0000| na        | na        | na        | na        |
>> > na        | na IPMI Watchdog    | 0x0        | discrete   | 0x0000|
>> na
>> > | na        | na        | na        | na        | na Physical Scrty
>> > | 0x0        | discrete   | 0x0000| na        | na        | na
>> > | na        | na        | na SMI Timeout      | 0x0        | discrete
>> > | 0x0000| na        | na        | na        | na        | na        |
>> > na System Event Log | 0x0        | discrete   | 0x0000| na        |
>> na
>> > | na        | na        | na        | na System Event     | 0x0
>> > | discrete   | 0x0000| na        | na        | na        | na        |
>> > na        | na
>> > P1 Status        | 0x0        | discrete   | 0x8000| na        | na
>> > | na        | na        | na        | na
>> > P1 VRD Hot       | 0x0        | discrete   | 0x0000| na        | na
>> > | na        | na        | na        | na CATERR           | 0x0
>> > | discrete   | 0x0000| na        | na        | na        | na        |
>> > na        | na CPU Missing      | 0x0        | discrete   | 0x0000|
>> na
>> > | na        | na        | na        | na        | na IOH Therm Trip
>> > | 0x0        | discrete   | 0x0000| na        | na        | na
>> > | na        | na        | na NM Capabilities  | na         | discrete
>> > | na    | na        | na        | na        | na        | na        |
>> > na
>> >
>> > As you can see above, 'Pwr Unit Status' is not available.
>> >
>> > Do I have to configure BMC?
>> > After BMC firmware update, I didn't change any configuration of BMC.
>> >
>> > Thanks,
>> >
>>
>> Please, keep the flow of the e-mail consistent as well as ipmitool-dev
>> in the loop, because that way you might get more answers and avoid
>> couple other things.
>>
>> Anyway, to your server. I don't have access to these, so it is hard to
say.
>> Yes, one option is to update BMC firmware, which should not reset its
>> settings(note: should not). I would check changelogs to see whether
>> there were some updates related to Power Supply or IPMI stack or alike.
>>
>> I'm not sure if any extra configuration of BMC is required, but again
>> I have no experience with these servers.
>>
>> I'll keep thinking about it, but I'm not sure what I could come up with.
>> Hmm if you check BMC/SP web interface, can you see readings of sensors
>> there? Can you see readings of power supply there?
>>
>> I'm sorry I was not much of help.
>>
>> Z.
>>
>> >
>> >
>> > -----Original Message-----
>> > From: Zdenek Styblik [mailto:zdenek.styb...@gmail.com]
>> > Sent: Wednesday, September 21, 2011 6:00 PM
>> > To: S. H. Lee
>> > Cc: ipmitool-devel@lists.sourceforge.net
>> > Subject: Re: [Ipmitool-devel] measuring the power consumption of a
>> > server
>> >
>> > On Tue, Sep 20, 2011 at 10:18 PM, S. H. Lee <smil...@korea.ac.kr>
wrote:
>> >> Hi,
>> >>
>> >> I have a SV7-2186 server with a S5500WBV motherboard and a Xeon
>> processor.
>> >> Its power supply is TDPS-600EB from DELTA.
>> >>
>> >> I am planning to develop a software checking the power consumption
>> >> of a server.
>> >>
>> >> According to some documents, the power consumption can be checked
>> >> through PSMI interface.
>> >>
>> >> Thus, I've tried to get the information by using ipmitool which can
>> >> read FRU data from a power supply.
>> >>
>> >> But, the fru command of ipmitool on my server only shows the FRU
>> >> data for a motherboard.
>> >>
>> >
>> > Hello,
>> >
>> > what is # ipmitool sdr list; or # ipmitool sdr list all; telling you?
>> > I have queried Sun/Oracle's
>> > X4170 and X4270m2 and both are showing /SYS/VPS and PSx readings.
>> > From
>> here I get the Nac Names and then I would query FRUs directly eg. #
>> ipmitool sensor reading /SYS/VPS; and stuff this data into RRD.
>> >
>> > Text above is just an example for inspiration and doesn't have to
>> necessarily work for you.
>> >
>> > Anyway, try 'sdr list' and you will see, or should see, what sensors
>> > you
>> can query for readings.
>> >
>> > Best regards,
>> > Zdenek
>> >
>> >>
>> >>
>> >> I want to know how to get the power consumption information of a
>> >> server by using IPMItool.
>> >>
>> >>
>> >>
>> >> Waiting for your reply and guidance.
>> >>
>> >>
>> >>
>> >> Thanks.
>> >>
>> >
>> >
>> >
>> >
>
>
>
>---------------------------------------------------------------------------
---
>All the data continuously generated in your IT infrastructure contains a
>definitive record of customers, application performance, security threats,
>fraudulent activity and more. Splunk takes this data and makes sense of it.
>Business sense. IT sense. Common sense.
>http://p.sf.net/sfu/splunk-d2dcopy1
>_______________________________________________
>Ipmitool-devel mailing list
>Ipmitool-devel@lists.sourceforge.net
>https://lists.sourceforge.net/lists/listinfo/ipmitool-devel
>
>

Attachment: smime.p7s
Description: S/MIME cryptographic signature

------------------------------------------------------------------------------
All the data continuously generated in your IT infrastructure contains a
definitive record of customers, application performance, security
threats, fraudulent activity and more. Splunk takes this data and makes
sense of it. Business sense. IT sense. Common sense.
http://p.sf.net/sfu/splunk-d2dcopy1
_______________________________________________
Ipmitool-devel mailing list
Ipmitool-devel@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/ipmitool-devel

Reply via email to