See Annotations Below

Norm
S/V Bandersnatch
Lying Julington Creek FL
N30 07.68 W081 38.47


----- Original Message ----- 
From: ahmet erkan 
To: [email protected]
Sent: 12/20/2010 11:04:05 PM 
Subject: Re: [Liveaboard] GALVANIC ISOLATOR


Hi Norm,
I am not sure if your questions have already been answered by the list but let 
me make an attempt anyway.

You asked :
"would you please address the issue of connecting (or not connecting) the ac 
neutral to earth."
IMO not connecting the ac neutral to earth would make the electrical system 
safe for the user making accidental contact with a hot conductor. However if 
the user begins to ignore the basic safety rules and becomes complacent about 
touching hot conductors he/she will be at the mercy of the system being fault 
free. Therefore a system with an isolated neutral ought to be checked 
frequently (preferably automatically) to verify all the current carrying 
conductors are indeed isolated from the chassis. 
Another shortcoming of the ungrounded neutral is you cannot use GFCI circuit 
breakers. 
One other shortcoming may be the increased vulnerability of your electronics to 
lightning. The isolation transformer that is providing the floating secondary 
neutral should be shielded (preferably both primary and secondary shields) and 
the shields should be hardwired to earth. 


Norm - Yes, I agree (and stated) that a way to check for ground faults would be 
a Good Thing.  Even a simple light bulb or meter.  

There is a shield on my isolation transformer between the windings and it is 
grounded to ship's ground.

I did try using a GFCI on the engine room circuit but the environment in the ER 
was too damp and it wouldn't hold.  I have not tried it elsewhere but I don't 
know why they wouldn't work.  

Even though the neutral is floating (on my boat), all the non-current carrying 
metal parts are still grounded.  

>From what I understand about lightening damage it is small voltages inside 
>sensitive electronics induced by the nearby heavy current flows from 
>lightening that does the most damage.



 
You asked :

"I believe in the US power that comes into a house is from a center tapped 
secondary winding in the pole transformer which delivers 240 vac at the ends of 
the coil and the neutral comes from the center tap.  The grounding of the 
neutral is only added in the house's breaker box by the neutral/grounding 
jumper wire.  Correct me if I am mistaken."
Correct, except I have never seen a jumper wire. The panels usually have a long 
aluminum block bolted to the chassis and it has a bunch of screw terminals for 
both neutral and ground wires.  US house wiring code requires both neutral 
(white) and ground (green) wires to be terminated to the chassis of the 
distribution panel/circuit breaker box. The chassis of the distribution panel 
is also routed (with a green wire) to a ground rod or a buried water pipe. I 
remember some Canadian folks on the list freaking out when they heard white 
neutral and green ground wires are bonded at the chassis of the panel but this 
is the way it is, and it makes sense to us.
 

Norm - My memory (such as it is) tells me that  the neutral terminal block in 
the US is insulated, the grounding block not insulated, and there is a wire 
connecting the two.  But I have made a note on my "To Do" list to have a look 
in a breaker box the next time I am in Lowes or Home Depot.  


You asked :
"I seem to have read that the European electrical system has ungrounded 
neutrals.  Is this true or not?"
In Turkey the houses are wired to one phase of the 220V Wye pole transformers 
with a pair of copper wires. One wire is hot and it has insulation, the other 
wire is the neutral and it is a bare copper conductor. The bare wire is bonded 
to the steel pipes that bring water to the house. The metal surfaces of the 
appliances are bonded to the bare neutral with a jumper and this jumper may be 
opened by the electrician to test the appliance for leakage. I believe the 
newer houses are using an insulated neutral and a bare ground wire so that GFCI 
devices can be used. The chassis to neutral jumper on the appliances are 
removed to be able to use the GFCI devices in bathrooms.
 
Cheers
Ahmet
 

Norm - Thank you for the great information about how it is done in Turkey.  It 
sounds safe to me and I'd bet Dr. Oz would approve it too.

 
_______________________________________________
Liveaboard mailing list
[email protected]
To adjust your membership settings over the web 
http://liveaboardonline.com/mailman/listinfo/liveaboard
To subscribe send an email to [email protected]

To unsubscribe send an email to [email protected]
The archives are at http://www.liveaboardonline.com/pipermail/liveaboard/

To search the archives http://www.mail-archive.com/[email protected]

The Mailman Users Guide can be found here 
http://www.gnu.org/software/mailman/mailman-member/index.html

Reply via email to