>"I did try using a GFCI on the engine room circuit but the environment in the 
>ER was too damp and it wouldn't hold.  
>I have not tried it elsewhere but I don't know why they wouldn't work.  
>Even though the neutral is floating (on my boat), all the non-current carrying 
>metal parts are still grounded."

With a "floating Neutral", the GFCI is going to detect a current from hot 
terminal through a person to earth and trip 
open only if the neutral insulation has also broken down to ground, similarly 
GFCI is going to detect a current from 
neutral through a person to earth and open only if the hot line insulation has 
also broken down to earth.  (I believe
Norm has also said this in different words)
If one wants to use GFCI devices with a floating Neutral, I suggest he/she (so 
PC) connects a 1uF capacitor from the 
hot line to ship's ground and another 1uF capacitor from the neutral to the 
ships ground. 
Both capacitors should be connected to the line side of the GFCI device. (ie: 
at the 120V secondary of your shielded 
 isolation transformer preferably close to the transformer for noise 
attenuation purposes) 
"60V is safer than 120V" in fact the 48V used by the phone company is actually 
the terminal voltage of a 
48V rated battery that is typically at  55V and could go to 60V during 
equalize. At the phone company we routinely 
worked on the 48V live equipment and touched the negative terminal (positive 
terminal is grounded for galvanic 
corrosion prevention) without worrying about getting electrocuted. 
So there you are, a +/-60Vac ships system with a GFCI protection device that 
will trip if there is more than 5mA 
imbalance between the hot or neutral currents and a little safer than your 
floating Neutral system. The imbalance 
will occur and interrupt the circuit either during a "heavy wet contact" by the 
user or if there is a fault in the system. 
The GFCI used in a grounded neutral system cannot detect Neutral to Ground type 
ground faults reliably 
due to lack of a supply to drive the current but the +/- 60V system should 
detect either Hot to ground or Neutral 
to ground insulation failures equally reliably. (Do test anyway)  
The capacitors should also work in tandem with the shield during lightning 
storms and provide common mode 
attenuation to voltage spikes in the order of 120dB. The capacitors should also 
work in tandem with the leakage 
inductance of the isolation transformer and provide normal mode attenuation to 
voltage spikes proportional to 
frequency of the disturbance.
Again, test for proper functionality of any system before relying on it for 
safety. 
This method of wiring is just a paper design at this time and has not been 
verified, I can verify using my isolation 
transformer and a GFCI receptacle or a CB from Home Depot and provide the 
results to the list if anyone wants 
to implement it?
BTW who is Dr. Oz?  A friend of George Orwell? I learn so many things on this 
list.
Fair winds
S/V 8827
Ahmet

 



From: [email protected]
To: [email protected]
Date: Sat, 25 Dec 2010 17:13:30 -0500
Subject: Re: [Liveaboard] GALVANIC ISOLATOR






See Annotations Below
 

Norm
S/V Bandersnatch
Lying Julington Creek FL
N30 07.68 W081 38.47
 
 

----- Original Message ----- 
From: ahmet erkan 
To: [email protected]
Sent: 12/20/2010 11:04:05 PM 
Subject: Re: [Liveaboard] GALVANIC ISOLATOR


Hi Norm,
I am not sure if your questions have already been answered by the list but let 
me make an attempt anyway.

You asked :
"would you please address the issue of connecting (or not connecting) the ac 
neutral to earth."
IMO not connecting the ac neutral to earth would make the electrical system 
safe for the user making accidental contact with a hot conductor. However if 
the user begins to ignore the basic safety rules and becomes complacent about 
touching hot conductors he/she will be at the mercy of the system being fault 
free. Therefore a system with an isolated neutral ought to be checked 
frequently (preferably automatically) to verify all the current carrying 
conductors are indeed isolated from the chassis. 
Another shortcoming of the ungrounded neutral is you cannot use GFCI circuit 
breakers. 
One other shortcoming may be the increased vulnerability of your electronics to 
lightning! . The isolation transformer that is providing the floating secondary 
neutral should be shielded (preferably both primary and secondary shields) and 
the shields should be hardwired to earth. 

 
Norm - Yes, I agree (and stated) that a way to check for ground faults would be 
a Good Thing.  Even a simple light bulb or meter.  
 
There is a shield on my isolation transformer between the windings and it is 
grounded to ship's ground.
 
I did try using a GFCI on the engine room circuit but the environment in the ER 
was too damp and it wouldn't hold.  I have not tried it elsewhere but I don't 
know why they wouldn't work.  
 
Even though the neutral is floating (on my boat), all the non-current carrying 
metal parts are still grounded.  
 
>From what I understand about lightening damage it is small voltages inside 
>sensitive electronics induced by the nearby heavy current flows from 
>lightening that does the most damage.
 
 
 
 
You asked :

"I believe in the US power that comes into a house is from a center tapped 
secondary winding in the pole transformer which delivers 240 vac at the ends of 
the coil and the neutral comes from the center tap.  The grounding of the 
neutral is only added in the house's breaker box by the neutral/grounding 
jumper wire.  Correct me if I am mistaken."
Correct, except I have never seen a jumper wire. The panels usually have a long 
aluminum block bolted to the chassis and it has a bunch of screw terminals for 
both neutral and ground wires.  US house wiring code requires both neutral 
(white) and ground (green) wires to be terminated to the chassis of the 
distribution panel/circuit breaker box. The chassis of the distribution panel 
is also routed (with a green wire) to a ground rod or a buried water pipe. I 
remember some Canadian folks on the list freaking out when they heard white 
neutral and green ground wires are bonded at the chassis of the panel but this 
is the way it is, and it makes sense to us.
 
 
Norm - My memory (such as it is) tells me that  the neutral terminal block in 
the US is insulated, the grounding block not insulated, and there is a wire 
connecting the two.  But I have made a note on my "To Do" list to have a look 
in a breaker box the next time I am in Lowes or Home Depot.  
 

You asked :
"I seem to have read that the European electrical system has ungrounded 
neutrals.  Is this true or not?"
In Turkey the houses are wired to one phase of the 220V Wye pole transformers 
with a pair of copper wires. One wire is hot and it has insulation, the other 
wire is the neutral and it is a bare copper conductor. The bare wire is bonded 
to the steel pipes that bring water to the house. The metal surfaces of the 
appliances are bonded to the bare neutral with a jumper and this jumper may be 
opened by the electrician to test the appliance for leakage. I believe the 
newer houses are using an insulated neutral and a bare ground wire so that GFCI 
devices can be used. The chassis to neutral jumper on the appliances are 
removed to be able to use the GFCI devices in bathrooms.
 
Cheers
Ahmet
 

Norm - Thank you for the great information about how it is done in Turkey.  It 
sounds safe to me and I'd bet Dr. Oz would approve it too.
 
 
_______________________________________________ Liveaboard mailing list 
[email protected] To adjust your membership settings over the web 
http://liveaboardonline.com/mailman/listinfo/liveaboard To subscribe send an 
email to [email protected] To unsubscribe send an email to 
[email protected] The archives are at 
http://www.liveaboardonline.com/pipermail/liveaboard/ To search the archives 
http://www.mail-archive.com/[email protected] The Mailman Users 
Guide can be found here 
http://www.gnu.org/software/mailman/mailman-member/index.html                   
                     
_______________________________________________
Liveaboard mailing list
[email protected]
To adjust your membership settings over the web 
http://liveaboardonline.com/mailman/listinfo/liveaboard
To subscribe send an email to [email protected]

To unsubscribe send an email to [email protected]
The archives are at http://www.liveaboardonline.com/pipermail/liveaboard/

To search the archives http://www.mail-archive.com/[email protected]

The Mailman Users Guide can be found here 
http://www.gnu.org/software/mailman/mailman-member/index.html

Reply via email to