Dear Iman,

With the load increasing, have you increase the generation from PV buses?  I 
don’t think the network loss could usually increase to nearly 10 times even at 
static limit. You may double the Pg on PV buses with the load. Then, if you 
still want to impose the branch thermal limits, you have to code the function 
to adjust the Pg for PV buses based on participant factors (branch flow 
sensitivity w.r.t. generation) or others.

 

Shiyang, Li

 

 

发件人: [email protected] 
[mailto:[email protected]] 代表 iman
发送时间: 2012年1月12日 0:57
收件人: [email protected]
主题: limits on the branches

 

Dear all,

 

I want to use power flow (PF) for the load increase studies. I picked 30 bus 
system with Pg=23.54 MW for the slack bus. Running the power flow with the base 
loads ,I get 25.97 MW which is quite close to 23.54.

Now I want to increase all of the loads 2 times. Running pf I get 236.55 MW for 
the slack bus .

I think in practice thermal line limits doesn’t allow this amount of power 
dragging from slack bus.

I want to make my problem practical by imposing thermal limits on the branches 
.How can I do that?

 

Thank you in advance for your patience 

I look forward to hear from you guys

Iman