*Dear Arash,Dear all,
*

*
*

*I-I read the power flow from line 1 to 2 and from line 1 to 3.After making
all the loads double, we have 154.81 and 81.74 MW for them respectively
(Baring in mind that they were 10.89 and 15.08 MW). Does that make sense?*

*
*

*II-I changed rate A or B or C from 133 to 60 but again got the same power
flow on branches 1-2 and 1-3.*

*
*

*III-If I am not able to do it by changing certain values, does anyone has
a reference to introduce to me in which I can calculate Line Thermal Limits
from x, r ,w ?*

*
*

*Thank you for your help *




On Wed, Jan 11, 2012 at 7:34 PM, Arash Alimardani <[email protected]
> wrote:

> I guess the thermal limit constraint is satisfied in your case (236.55 MW).
> Firstly, you have to read the power flow through the line, not the
> injected power in one bus.
> Secondly, as I remember, the column rateA in the branch matrix for each
> case is the thermal limit of that line.
> In your case, the slack is connected to bus 2 and bus 3, which provides it
> with 260 MW capacity of transmitting power.
>
> Regards
>
>
> On Wed, Jan 11, 2012 at 8:57 AM, iman <[email protected]> wrote:
>
>> Dear all,
>>
>>
>> I want to use power flow (PF) for the load increase studies. I picked 30
>> bus system with Pg=23.54 MW for the slack bus. Running the power flow with
>> the base loads ,I get 25.97 MW which is quite close to 23.54.
>>
>> Now I want to increase all of the loads 2 times. Running pf I get 236.55
>> MW for the slack bus .
>>
>> I think in practice thermal line limits doesn’t allow this amount of
>> power dragging from slack bus.
>>
>> I want to make my problem practical by imposing thermal limits on the
>> branches .How can I do that?
>>
>>
>> Thank you in advance for your patience
>>
>> I look forward to hear from you guys
>>
>> Iman
>>
>
>


-- 
Best regards
Iman