Dear Shiyang, Li

Thanks for taking time answering.

I didn’t increase any generations in the PV buses because my objective for
increasing the load is pushing the system to the instability margin (like
voltage drop in buses).

I agree with you that network loss doesn’t seem a real number as well as
other numbers.

In the case30.m (base case) after running pf I have:

*Total generation capacity =335 MW*

*On-line capacity =335 MW*

*Continued Gens (actual generation)=191.6 MW*

*Load = 189.2 MW*

*Losses=2.44 MW*

* *

*Branch 1-2 =10.89 MW*

*Branch 1-3=15.08 MW*

****Now I multiply Pd (demanded power)by 2 to make the whole consumption
twice, I have***

*Total generation capacity =815 MW*

*On-line capacity =815 MW*

*Continued Gens (actual generation)=402.2 MW*

*Load = 378 MW*

*Losses=23.82 MW*

* *

*Branch 1-2 =154.81 MW*

*Branch 1-3=81.08 MW*

* *

* *

Having said the above in brief:

1-In Bus 1 (Slack) we have 236.55 MW injection power .Where does this added
amount come from?

2-What if I want to fix branch 1-2 limit to 100 MW (or 100 MVA)? What
should I do?



Thank you for your attention and time

Wish you the best.

Iman


On Wed, Jan 11, 2012 at 7:45 PM, 李诗旸 <[email protected]> wrote:

> Dear Iman,****
>
> With the load increasing, have you increase the generation from PV buses?
>  I don’t think the network loss could usually increase to nearly 10 times
> even at static limit. You may double the Pg on PV buses with the load.
> Then, if you still want to impose the branch thermal limits, you have to
> code the function to adjust the Pg for PV buses based on participant
> factors (branch flow sensitivity w.r.t. generation) or others.****
>
> ** **
>
> Shiyang, Li****
>
> ** **
>
> ** **
>
> *发件人:* [email protected] [mailto:
> [email protected]] *代表 *iman
> *发送时间:* 2012年1月12日 0:57
> *收件人:* [email protected]
> *主题:* limits on the branches****
>
> ** **
>
> Dear all,****
>
> ** **
>
> I want to use power flow (PF) for the load increase studies. I picked 30
> bus system with Pg=23.54 MW for the slack bus. Running the power flow with
> the base loads ,I get 25.97 MW which is quite close to 23.54.****
>
> Now I want to increase all of the loads 2 times. Running pf I get 236.55
> MW for the slack bus .****
>
> I think in practice thermal line limits doesn’t allow this amount of power
> dragging from slack bus.****
>
> I want to make my problem practical by imposing thermal limits on the
> branches .How can I do that?****
>
> ** **
>
> Thank you in advance for your patience ****
>
> I look forward to hear from you guys****
>
> Iman****
>



-- 
Best regards
Iman