*Dear Dr Zimmerman, Shiyang, Li and Arash*

Thank you for your reply to my problem. Dr Zimmerman has said that I need
to use OPF *instead of PF* for branch thermal constraints. The problem is
that I am using another optimization method connected to Matpower and this
optimization program only needs to use V,P,Q and delta values from the
power flow calculations. In my optimization program, I am trying to
minimize P loss and other things so if I use OPF, my final results would be
affected and they are not purely from my optimization method.

I also tried to code the thermal limit for PF myself but I haven’t been
able to.

 *Would you please help me in coding the thermal constraints?*


Regards

Iman


2012/1/13 新浪VIP <[email protected]>

> Hi Iman,
> 1, Even your object is to study the system near static limit, keeping all
> generation of PV buses is usually not reasonable, because this scenario may
> never occur.  For this sake, when we calculate load margin for example, we
> normally increase P generation with loads.
>
> 2, Power is always conserved on static state. Without PV generation
> increasing
> , the slack bus has to compensate all the deficit, 236.55 MW here.
>
> 3, Like what Dr Ray said, if you want to involve thermal limits of
> branches, you may either use OPF solver, or code you own function to adjust
> PV generations.
>
> Shiyang Li
>
> 发自我的 iPhone
>
> 在 2012-1-12,21:44,iman <[email protected]> 写道:
>
> Dear Shiyang, Li
>
> Thanks for taking time answering.
>
> I didn’t increase any generations in the PV buses because my objective for
> increasing the load is pushing the system to the instability margin (like
> voltage drop in buses).
>
> I agree with you that network loss doesn’t seem a real number as well as
> other numbers.
>
> In the case30.m (base case) after running pf I have:
>
> *Total generation capacity =335 MW*
>
> *On-line capacity =335 MW*
>
> *Continued Gens (actual generation)=191.6 MW*
>
> *Load = 189.2 MW*
>
> *Losses=2.44 MW*
>
> * *
>
> *Branch 1-2 =10.89 MW*
>
> *Branch 1-3=15.08 MW*
>
> ****Now I multiply Pd (demanded power)by 2 to make the whole consumption
> twice, I have***
>
> *Total generation capacity =815 MW*
>
> *On-line capacity =815 MW*
>
> *Continued Gens (actual generation)=402.2 MW*
>
> *Load = 378 MW*
>
> *Losses=23.82 MW*
>
> * *
>
> *Branch 1-2 =154.81 MW*
>
> *Branch 1-3=81.08 MW*
>
> * *
>
> * *
>
> Having said the above in brief:
>
> 1-In Bus 1 (Slack) we have 236.55 MW injection power .Where does this
> added amount come from?
>
> 2-What if I want to fix branch 1-2 limit to 100 MW (or 100 MVA)? What
> should I do?
>
>
>
> Thank you for your attention and time
>
> Wish you the best.
>
> Iman
>
>
> On Wed, Jan 11, 2012 at 7:45 PM, 李诗旸 <[email protected]> wrote:
>
>> Dear Iman,****
>>
>> With the load increasing, have you increase the generation from PV buses?
>>  I don’t think the network loss could usually increase to nearly 10 times
>> even at static limit. You may double the Pg on PV buses with the load.
>> Then, if you still want to impose the branch thermal limits, you have to
>> code the function to adjust the Pg for PV buses based on participant
>> factors (branch flow sensitivity w.r.t. generation) or others.****
>>
>> ** **
>>
>> Shiyang, Li****
>>
>> ** **
>>
>> ** **
>>
>> *发件人:* [email protected] [mailto:
>> [email protected]] *代表 *iman
>> *发送时间:* 2012年1月12日 0:57
>> *收件人:* [email protected]
>> *主题:* limits on the branches****
>>
>> ** **
>>
>> Dear all,****
>>
>> ** **
>>
>> I want to use power flow (PF) for the load increase studies. I picked 30
>> bus system with Pg=23.54 MW for the slack bus. Running the power flow with
>> the base loads ,I get 25.97 MW which is quite close to 23.54.****
>>
>> Now I want to increase all of the loads 2 times. Running pf I get 236.55
>> MW for the slack bus .****
>>
>> I think in practice thermal line limits doesn’t allow this amount of
>> power dragging from slack bus.****
>>
>> I want to make my problem practical by imposing thermal limits on the
>> branches .How can I do that?****
>>
>> ** **
>>
>> Thank you in advance for your patience ****
>>
>> I look forward to hear from you guys****
>>
>> Iman****
>>
>
>
>
> --
> Best regards
> Iman
>
>


-- 
Best regards
Iman