For the question asked by simone coche, i found some answer from the forum. 
From that i understand that PV generator can be added as a PQ bus with negative 
load. Is it correct or not?

You can do it either way. It will not change the solution algorithm. I like the 
way I suggested because the power flow output will have all the generators 
together in the gen struct.

Also for my research i want to have data for the indian system (MV radial 
network) Where can i get the data?  can any one help me?

MATPOWER is not the correct forum to ask "where can I get data for xyz system". 
Please refrain from asking such questions in the future.

Shri


On Thursday, 17 July 2014 12:28 AM, "Abhyankar, Shrirang G." 
<[email protected]<mailto:[email protected]>> wrote:


Simone,
   Add your generator in the gen data struct in the case file and set its bus 
type to PQ.

Shri

On Jul 16, 2014, at 8:31 AM, "Simone Cochi" 
<[email protected]<mailto:[email protected]>> wrote:

Dear all,
I’m completely new to the power systems simulation. I want to simulate the 
effect of photovoltaic generator on a MV radial network and in particular the 
rise of voltage profile that this generators involve. If I insert the 
photovoltaic generators as PV nodes, the voltage at this busses will be fixed 
so I can’t see the effect on voltage and I thought that I could insert them as 
PQ node with negative load. Do you think that this is feasible?

Thanks
--
Simone