It depends on what you want to do. If you are running opf you need to set your Qmin = Qmax = 0 or whatever your reactive load might be. If you are doing power flow I think that you might have difficult time with the generator emulating load supplying reactive power.
Jovan Ilic On Thu, Jul 17, 2014 at 1:18 AM, ambi ka <[email protected]> wrote: > Sir, > For the question asked by simone coche, i found some answer from the > forum. From that i understand that PV generator can be added as a PQ bus > with negative load. Is it correct or not? > Also for my research i want to have data for the indian system (MV radial > network) Where can i get the data? can any one help me? > > > On Thursday, 17 July 2014 12:28 AM, "Abhyankar, Shrirang G." < > [email protected]> wrote: > > > Simone, > Add your generator in the gen data struct in the case file and set its > bus type to PQ. > > Shri > > On Jul 16, 2014, at 8:31 AM, "Simone Cochi" <[email protected]> wrote: > > Dear all, > I’m completely new to the power systems simulation. I want to simulate > the effect of photovoltaic generator on a MV radial network and in > particular the rise of voltage profile that this generators involve. If I > insert the photovoltaic generators as PV nodes, the voltage at this busses > will be fixed so I can’t see the effect on voltage and I thought that I > could insert them as PQ node with negative load. Do you think that this is > feasible? > > Thanks > -- > Simone > Sent with Airmail > > > >