Thanks for correcting me.  I agree with your explanation.

Shri

From: Ray Zimmerman <[email protected]<mailto:[email protected]>>
Reply-To: MATPOWER discussion forum 
<[email protected]<mailto:[email protected]>>
Date: Thu, 16 Oct 2014 15:43:54 -0400
To: MATPOWER discussion forum 
<[email protected]<mailto:[email protected]>>
Subject: Re: Generators as negative loads

Simone and Shri,

I’ve looked at this a bit and I’m not sure I agree. First of all, Simone, I 
can’t seem to create a case that demonstrates what you are seeing (unless by “a 
little reactive power output” you mean something non-zero on the order of the 
termination tolerances. So, could you please send me a small example off-list?

And Shri, while I agree there is a small bug in the handling of generator 
reactive power at PQ buses, I don’t think it has anything to do with the 
charging capacitance of connected lines. In fact, I think the total reactive 
power injection at the bus is correct. The only issue is that the total is 
distributed proportionally among all of the generators at the bus, as opposed 
to leaving the allocations as specified in the input. In any case, I think your 
suggested patch will not be correct, since gbus and on could then be of 
different dimension.

Let me know if you still think I’m missing something,

    Ray


On Oct 8, 2014, at 2:46 PM, Abhyankar, Shrirang G. 
<[email protected]<mailto:[email protected]>> wrote:

Simone,
  I think the smallish reactive power output from the generator that you
are seeing is due to the reactive power supplied by the line charging
capacitance(s) of the transmission line(s) connected to it.  Instead of
what I suggested earlier, you could set the generator output as negative
load in the bus data struct (and set its bus type to PQ).

@Ray: I think the proper fix for this is by applying the following patch
in pfsoln.m that excludes generators at PQ buses from gbus.

 - gbus = gen(on, GEN_BUS);                %% what buses are they at?
 + gbus = find(bus(gen(on,GEN_BUS),BUS_TYPE)~=PQ)  %% Only include
generator buses with types PV and REF.


Shri

-----Original Message-----
From: Simone Cochi <[email protected]<mailto:[email protected]>>
Reply-To: MATPOWER discussion forum 
<[email protected]<mailto:[email protected]>>
Date: Wed, 8 Oct 2014 16:01:05 +0200
To: MATPOWER discussion forum 
<[email protected]<mailto:[email protected]>>
Subject: Generators as negative loads

Hello there,
I asked months ago if I could simulate photovoltaic generators as PQ
negative loads in order to see the the voltage profile modifications
caused by injection of the generators.Someone advised me to put the
generator in the generator struct and to mark bus type as PQ (1). I
notice that even if I put reactive power output to zero in the
generator and bus struct, I have a little a little reactive power
output from the photovoltaic generator in the results. Someone can
explain me this behaviour?

Thank you very much

Simone





Reply via email to