Thank you very much for the answer Sir, I tried your suggestion and it
seems to work pretty well. I’ll compare the results with the ones
provided by different software and let the community knows.

2014-07-17 16:00 GMT+02:00 Abhyankar, Shrirang G. <[email protected]>:
>
> On Jul 16, 2014, at 10:19 PM, "ambi ka" <[email protected]> wrote:
>
> Sir,
> For the question asked by simone coche, i found some answer from the forum.
> From that i understand that PV generator can be added as a PQ bus with
> negative load. Is it correct or not?
>
>
> You can do it either way. It will not change the solution algorithm. I like
> the way I suggested because the power flow output will have all the
> generators together in the gen struct.
>
> Also for my research i want to have data for the indian system (MV radial
> network) Where can i get the data?  can any one help me?
>
>
> MATPOWER is not the correct forum to ask "where can I get data for xyz
> system". Please refrain from asking such questions in the future.
>
> Shri
>
>
>
> On Thursday, 17 July 2014 12:28 AM, "Abhyankar, Shrirang G."
> <[email protected]> wrote:
>
>
> Simone,
>    Add your generator in the gen data struct in the case file and set its
> bus type to PQ.
>
> Shri
>
> On Jul 16, 2014, at 8:31 AM, "Simone Cochi" <[email protected]> wrote:
>
> Dear all,
> I’m completely new to the power systems simulation. I want to simulate the
> effect of photovoltaic generator on a MV radial network and in particular
> the rise of voltage profile that this generators involve. If I insert the
> photovoltaic generators as PV nodes, the voltage at this busses will be
> fixed so I can’t see the effect on voltage and I thought that I could insert
> them as PQ node with negative load. Do you think that this is feasible?
>
> Thanks
> --
> Simone
> Sent with Airmail
>
>
>