Gelli,
  I'm not sure whether you have turned on the option pf.enforce_q_lims (help 
mpoption) to enforce Q limits for the power flow solver.

  Q limits should be applied once the power flow is at, or fairly close, to an 
"actual" solution. If the limits are imposed during the Newton (or gausspf) 
iterations [the initial iterates may not be close to the actual solution] then 
there may be potential solver stability issue. MATPOWER could possibly 
incorporate some logic for handling Q limits in the routines (Newton, 
Gauss-Siedel, Fast-Decoupled) called by runpf() but then it is a headache for 
code maintenance as now any change to the logic has to be replicated in all the 
routines!

Shri

From: Gelli Ravikumar 
<[email protected]<mailto:[email protected]>>
Reply-To: MATPOWER discussion forum 
<[email protected]<mailto:[email protected]>>
Date: Fri, 22 Aug 2014 14:31:29 +0530
To: MATPOWER discussion forum 
<[email protected]<mailto:[email protected]>>
Subject: Re: Type switching of PV buses to PQ buses with reference to Q limits 
in Load flow

The concepts are well known for handling the switching mechanism of PV to PQ 
while executing load flow programs. But, my question is that: This was not 
tackled in the gausspf.m and newtonpf.m of the MatPower package, just have a 
glimpse over those load flow programs. However, these functions are used to 
call from the runpf.m. If you observed the runpf.m prgram, after the power-flow 
solution obtained from any of the  "PF_ALG"s, the q limits check have been done 
to just intimate the users as a message like the limits are violated.




--
with Regards
----------------------------------------------------
Gelli Ravikumar
Research Scholar (Ph.D),
Field Computations Lab,
Dept. of Electrical Engineering,
IIT Bombay, Powai, Mumbai 400076
Ph: 022-2576 4424, 089 765 983 96

Gandhian Young Technological Innovation Award - 2013
POSOCO Power System Award: PPSA - 2013
IITB PhD Executive Member - 2013-14
IITB SARC Core Technical Member - 2014-15




On Fri, Aug 22, 2014 at 2:15 PM, Priyanka Murali 
<[email protected]<mailto:[email protected]>> wrote:
You will have to change the type of the bus when Q hits the limits. For this 
monitor the Q limit and when it hits write call a function for this.


On Fri, Aug 22, 2014 at 2:07 PM, Gelli Ravikumar 
<[email protected]<mailto:[email protected]>> wrote:
Dear Sir/s,


I have gone through core load flow programs of MatPower such as gausspf.m and 
newtonpf.m. But, in these methods, I could not found any provision of switching 
the PV bus to PQ bus whenever the Q limits of PV bus not met in the duration of 
iterations. Please let me know your insights into it.



--
with Regards
----------------------------------------------------
Gelli Ravikumar
Research Scholar (Ph.D),
Field Computations Lab,
Dept. of Electrical Engineering,
IIT Bombay, Powai, Mumbai 400076
Ph: 022-2576 4424, 089 765 983 96

Gandhian Young Technological Innovation Award - 2013
POSOCO Power System Award: PPSA - 2013
IITB PhD Executive Member - 2013-14
IITB SARC Core Technical Member - 2014-15




Reply via email to