But you did that, it would no longer be a powerflow calculation.  There are
good mathematical reasons why the standard powerflow calculation is
formulated so that there should be at least one swing bus (where you
specify both V and A, leaving P and Q "free").  If you specified V, A, and
Pgen at the swing, this would yield an overdetermined system.  You could
theoretically formulate a powerflow in which the swing bus specified only A
(the global angle reference) and Pgen, leaving Vref and Qgen free, but this
would yield a system of equations with a severe pathology, namely a
near-singular Jacobian (this originates from the fact that the full
transmission admittance matrix, being a Laplacian matrix, always has a zero
eigenvalue, which corresponds to a translation symmetry consisting in
uniformly shifting all voltages;  pinning down at least one voltage is what
breaks this symmetry and recovers invertibility).

However, I think you're right it would be a good idea to *warn* the user
when the swing generator(s) have gone over their PMAX (or below their
PMIN!).

-- 
Jose L. Marin
Grupo AIA


On Thu, Feb 18, 2016 at 12:08 AM, Jovan Ilic <[email protected]> wrote:

>
> Good point, maybe we should trow a Pgen constraint on the swing buses in
> the Jacobian.
>
>
>
> On Wed, Feb 17, 2016 at 5:30 PM, Santiago Torres <[email protected]>
> wrote:
>
>> Because the exceding generation is supplied by the swing bus. Normal
>> power flow does not check power generation limits.
>> El 17 feb. 2016 1:58 PM, "Bai, Wenlei" <[email protected]> escribió:
>>
>>> Dear Ray,
>>>
>>> I tried to modified load of ‘case9’ to exceed the total generation
>>> capacity purposely.
>>>
>>> To my surprise, power flow still converges.  More specifically,  the
>>> total generator ‘on-line capacity’ is 820MW, while the ‘actual generation’
>>> is 920.8MW
>>>
>>> Why the actual generation can be larger than its capacity?
>>>
>>>
>>>
>>> Blessings,
>>> Wenlei
>>>
>>>
>>>
>>
>