I’m not sure I understand your question. But you will need to run a power flow 
or OPF on island 1 in order to have a valid power flow solution with matching 
load and generation.

   Ray


> On Jul 6, 2017, at 3:39 AM, prem panigrahi <[email protected]> wrote:
> 
> Dear Ray Sir
>               In my case i have 4 Island and remove the buses of 3 Island 
> having no generation and the Island 1 have a reference bus.  In generation 
> side dispatched load is less than the capacity due to which there is a 
> mismatch in load and generation. Is it a natural case or I can manually 
> increase the dispatch load from generation unit.
> 
> 
> 
> 
> 
> [GROUPS, ISOLATED] = case_info(mpc)
> Checking connectivity ... 4 connected groups, 4 isolated buses
> Elapsed time is 0.034766 seconds.
> ================================================================================
>                         Full       Island      Island      Island      Island 
>   
>                        System         1           2           3           4   
>   
> Number of:           ----------  ----------  ----------  ----------  
> ---------- 
>   buses                    57          45           3           3           2 
>   
>   loads                    42          35           2           1           2 
>   
>     on                     42          35           2           1           2 
>   
>     off                     -           -           -           -           - 
>   
>     fixed                  42          35           2           1           2 
>   
>     dispatchable            -           -           -           -           - 
>   
>       on                    -           -           -           -           - 
>   
>       off                   -           -           -           -           - 
>   
>   generators                7           7           -           -           - 
>   
>     on                      7           7           -           -           - 
>   
>     off                     -           -           -           -           - 
>   
>   shunt elements            3           2           1           -           - 
>   
>   branches                 80          59           3           2           1 
>   
>     on                     61          55           3           2           1 
>   
>     off                    19           4           -           -           - 
>   
>     ties (off)             14          12           4           3           2 
>   
> 
> Load                
>   active (MW)       
>     dispatched           1375.9      1321.9        33.6         2.5         
> 5.9 
>       fixed              1375.9      1321.9        33.6         2.5         
> 5.9 
>       dispatchable          -           -           -           -           - 
>   
>     nominal              1375.9      1321.9        33.6         2.5         
> 5.9 
>       on                 1375.9      1321.9        33.6         2.5         
> 5.9 
>       off                   -           -           -           -           - 
>   
>       fixed              1375.9      1321.9        33.6         2.5         
> 5.9 
>       dispatchable          -           -           -           -           - 
>   
>         on                  -           -           -           -           - 
>   
>         off                 -           -           -           -           - 
>   
>   reactive (MVAr)   
>     dispatched            336.4       317.5        10.4         1.0         
> 2.7 
>       fixed               336.4       317.5        10.4         1.0         
> 2.7 
>       dispatchable          -           -           -           -           - 
>   
>     nominal               336.4       317.5        10.4         1.0         
> 2.7 
>       on                  336.4       317.5        10.4         1.0         
> 2.7 
>       off                   -           -           -           -           - 
>   
>       fixed               336.4       317.5        10.4         1.0         
> 2.7 
>       dispatchable          -           -           -           -           - 
>   
>         on                  -           -           -           -           - 
>   
>         off                 -           -           -           -           - 
>   
> 
> Generation          
>   active (MW)       
>     dispatched            928.9       928.9         -           -           - 
>   
>     max capacity         1975.9      1975.9         -           -           - 
>   
>       on                 1975.9      1975.9         -           -           - 
>   
>       off                   -           -           -           -           - 
>   
>     min capacity            -           -           -           -           - 
>   
>       on                    -           -           -           -           - 
>   
>       off                   -           -           -           -           - 
>   
>   reactive (MVAr)   
>     dispatched            193.3       193.3         -           -           - 
>   
>     max capacity          699.0       699.0         -           -           - 
>   
>       on                  699.0       699.0         -           -           - 
>   
>       off                   -           -           -           -           - 
>   
>     min capacity         -468.0      -468.0         -           -           - 
>   
>       on                 -468.0      -468.0         -           -           - 
>   
>       off                   -           -           -           -           - 
>   
> 
> Shunt Injections    
>     active (MW)             -           -           -           -           - 
>   
>     reactive (MVAr)        21.6        11.6        10.0         -           - 
>   
> 
> Branch Losses       
>     active (MW)             -           -           -           -           - 
>   
>     reactive (MVAr)         -           -           -           -           - 
>   
> 
> DC line             
>   export (MW)       
>     dispatch                -           -           -           -           - 
>   
>     max capacity            -           -           -           -           - 
>   
>       on                    -           -           -           -           - 
>   
>       off                   -           -           -           -           - 
>   
>     min capacity            -           -           -           -           - 
>   
>       on                    -           -           -           -           - 
>   
>       off                   -           -           -           -           - 
>   
> 
> Reference Buses     
>   num of ref buses          1           1           0           0           0 
>   
>   ref bus numbers           1           1                                     
>   
> 
> 
> --------------------------------------------------------------------------------
>                       Isolated  
>                         Buses   
> Number of:           ---------- 
>   buses                     4   
>   loads                     2   
>     on                      2   
>     off                     -   
>     fixed                   2   
>     dispatchable            -   
>       on                    -   
>       off                   -   
>   generators                -   
>     on                      -   
>     off                     -   
>   shunt elements            -   
>   branches                  -   
>     on                      -   
>     off                     -   
>     ties (off)              7   
> 
> Load                
>   active (MW)       
>     dispatched             12.0 
>       fixed                12.0 
>       dispatchable          -   
>     nominal                12.0 
>       on                   12.0 
>       off                   -   
>       fixed                12.0 
>       dispatchable          -   
>         on                  -   
>         off                 -   
>   reactive (MVAr)   
>     dispatched              4.8 
>       fixed                 4.8 
>       dispatchable          -   
>     nominal                 4.8 
>       on                    4.8 
>       off                   -   
>       fixed                 4.8 
>       dispatchable          -   
>         on                  -   
>         off                 -   
> 
> Generation          
>   active (MW)       
>     dispatched              -   
>     max capacity            -   
>       on                    -   
>       off                   -   
>     min capacity            -   
>       on                    -   
>       off                   -   
>   reactive (MVAr)   
>     dispatched              -   
>     max capacity            -   
>       on                    -   
>       off                   -   
>     min capacity            -   
>       on                    -   
>       off                   -   
> 
> Shunt Injections    
>     active (MW)             -   
>     reactive (MVAr)         -   
> 
> Branch Losses       
>     active (MW)             -   
>     reactive (MVAr)         -   
> 
> DC line             
>   export (MW)       
>     dispatch                -   
>     max capacity            -   
>       on                    -   
>       off                   -   
>     min capacity            -   
>       on                    -   
>       off                   -   
> 
> Reference Buses     
>   num of ref buses          0   
>   ref bus numbers             
> 
> From: [email protected] 
> <mailto:[email protected]> 
> <[email protected] 
> <mailto:[email protected]>> on behalf of Ray 
> Zimmerman <[email protected] <mailto:[email protected]>>
> Sent: Monday, July 3, 2017 9:15:52 PM
> To: MATPOWER discussion forum
> Subject: Re: DCOPF not converge
>  
> Hi Prem,
> 
> If you are solving each island individually, the DC OPF should converge as 
> long as (1) you have a reference bus in the island, (2) there is adequate 
> generation to cover the load in the island, and (3) the line constraints do 
> not prevent the generated power from reaching the loads.
> 
>    Ray
> 
> 
>> On Jun 23, 2017, at 9:18 AM, prem panigrahi <[email protected] 
>> <mailto:[email protected]>> wrote:
>> 
>> 
>> Dear All
>>            I am facing convergence problem during the calculation of DCOPF 
>> in IEEE  buses. For my work I have fixed the capacity of transmission line 
>> 110% of initial power flow by changing the RATE_A field, then at each time, 
>> I increase the load and generation with a factor (1+alpha). I remove the 
>> lines whose power flow is more than their capacity.  After the certain load, 
>> the grid divided into many parts. I tried to solve the island problem but 
>> dcopf not converged. I found on one island the dispatchable load is less 
>> than its generation. Should I take this situation as a blackout??.  Please 
>> help me
>>  
>>  
>>  
>>  
>>  
>>  
>>  
>>  
>> Prem Panigrahi
>> Research Scholar
>> India
>>  
>> 
>> 
>> From: prem panigrahi <[email protected] 
>> <mailto:[email protected]>>
>> Sent: Tuesday, June 20, 2017 6:13:37 PM
>> To: [email protected] <mailto:[email protected]>
>> Subject: DCOPF not converge
>>  
>> Hello  Sir
>> 
>> In IEEE 57 bus, I fixed the capacity of transmission line and then increase 
>> the load and generation. I removed those lines whose power flow is more than 
>> their capacities. When the grid is divided into 4 parts. I remove the 
>> isolated buses. In island 1-------  45 buses are there including  7 
>> generators. Matpower automatically considers the slack bus. But the DCOPF 
>> doesn't converge as the generation has a capacity of 1975.9 MW, but it 
>> dispatches only 928.9 MW. So there is a mismatch in load and generation. 
>> Load requirement is 1321.9 MW. Is there any mistake that I am doing? . 
>> <result.txt>