I'm not sure, but I think the heat strips are sized according to the airflow 
the air handler can provide.    Too big, they will either have a short life and 
burn out, or start a fire and burn down your house.
-- 
Max Dillon
Charleston SC
'87 300TD
'95 E300

On January 8, 2017 8:46:07 PM EST, "Kaleb C. Striplin via Mercedes" 
<[email protected]> wrote:
>In looking at the sticker on the air handler there is a list of a bunch
>
>of different heater kits that can be installed and they were supposed
>to 
>mark which one was installed.  Well nothing is marked.  I am suspecting
>
>maybe the kit that is installed is possibly too big for the circuit.  I
>
>need to pull the cover sometime and see if I can tell which heater is 
>installed.  Anyway it is on a 60 amp breaker and I have 6 gauge wire 
>running to the unit (2 60 amp circuits actually, one goes to the air 
>handler other to the heater kit).  I am looking at the chart and
>wanting 
>to make sure I am reading correctly what the biggest heater I can have 
>for the circuit.  There are different heater types based on if it is a 
>single or multiple circuit.  Since I have 2 60 amp circuits going to
>the 
>unit, one for air handler and one for aux heater, is this considered a 
>multiple circuit setup, or single since 2 circuit goes to the actual 
>heater?
>
>
>There is also a spec for circuit amps, min circuit ampacity, and
>maximum 
>circuit protection.  For example one heater kit listed on the chart is
>a 
>single circuit model, KW is listed at 7.2/9.6 which is 2 elements at
>4.8 
>each, circuit amps is listed at 34.6/40, min ampacity 49/56, max amp 
>circuit protection 50/60.  So this is just a random model I selected 
>from the list and am I reading it correctly that this kit basically 
>needs a 60 amp circuit to run it?
>
>I am just trying to get an idea on if I am reading the spec chart 
>correct then will figure out which heater is actually installed so on 
>and so forth
>
>
>
>
>On 1/8/2017 3:37 PM, Max Dillon via Mercedes wrote:
>> I don't know how you conclude that, it sounds like when your system
>goes into defrost, the heat strips are turned on, and the breaker for
>those trips off.  Outside unit then shuts off because the heat strips
>are off, so defrost mode won't work.  Solve the breaker trip issue -
>heater strips over sized?
>
>
>_______________________________________
>http://www.okiebenz.com
>
>To search list archives http://www.okiebenz.com/archive/
>
>To Unsubscribe or change delivery options go to:
>http://mail.okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
_______________________________________
http://www.okiebenz.com

To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://mail.okiebenz.com/mailman/listinfo/mercedes_okiebenz.com

Reply via email to