They have a 5 ton only model listed on the chart and I have a 5 ton unit so I 
am guessing that is the one I should have.  I was
Just wondering about the difference between what they are calling single and 
multiple circuit. The kit listed for 5 ton only says it's multiple circuit so 
that probably answers my question. 

Sent from my iPhone

> On Jan 8, 2017, at 8:27 PM, Max Dillon via Mercedes <[email protected]> 
> wrote:
> 
> I'm not sure, but I think the heat strips are sized according to the airflow 
> the air handler can provide.    Too big, they will either have a short life 
> and burn out, or start a fire and burn down your house.
> -- 
> Max Dillon
> Charleston SC
> '87 300TD
> '95 E300
> 
>> On January 8, 2017 8:46:07 PM EST, "Kaleb C. Striplin via Mercedes" 
>> <[email protected]> wrote:
>> In looking at the sticker on the air handler there is a list of a bunch
>> 
>> of different heater kits that can be installed and they were supposed
>> to 
>> mark which one was installed.  Well nothing is marked.  I am suspecting
>> 
>> maybe the kit that is installed is possibly too big for the circuit.  I
>> 
>> need to pull the cover sometime and see if I can tell which heater is 
>> installed.  Anyway it is on a 60 amp breaker and I have 6 gauge wire 
>> running to the unit (2 60 amp circuits actually, one goes to the air 
>> handler other to the heater kit).  I am looking at the chart and
>> wanting 
>> to make sure I am reading correctly what the biggest heater I can have 
>> for the circuit.  There are different heater types based on if it is a 
>> single or multiple circuit.  Since I have 2 60 amp circuits going to
>> the 
>> unit, one for air handler and one for aux heater, is this considered a 
>> multiple circuit setup, or single since 2 circuit goes to the actual 
>> heater?
>> 
>> 
>> There is also a spec for circuit amps, min circuit ampacity, and
>> maximum 
>> circuit protection.  For example one heater kit listed on the chart is
>> a 
>> single circuit model, KW is listed at 7.2/9.6 which is 2 elements at
>> 4.8 
>> each, circuit amps is listed at 34.6/40, min ampacity 49/56, max amp 
>> circuit protection 50/60.  So this is just a random model I selected 
>> from the list and am I reading it correctly that this kit basically 
>> needs a 60 amp circuit to run it?
>> 
>> I am just trying to get an idea on if I am reading the spec chart 
>> correct then will figure out which heater is actually installed so on 
>> and so forth
>> 
>> 
>> 
>> 
>>> On 1/8/2017 3:37 PM, Max Dillon via Mercedes wrote:
>>> I don't know how you conclude that, it sounds like when your system
>> goes into defrost, the heat strips are turned on, and the breaker for
>> those trips off.  Outside unit then shuts off because the heat strips
>> are off, so defrost mode won't work.  Solve the breaker trip issue -
>> heater strips over sized?
>> 
>> 
>> _______________________________________
>> http://www.okiebenz.com
>> 
>> To search list archives http://www.okiebenz.com/archive/
>> 
>> To Unsubscribe or change delivery options go to:
>> http://mail.okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> _______________________________________
> http://www.okiebenz.com
> 
> To search list archives http://www.okiebenz.com/archive/
> 
> To Unsubscribe or change delivery options go to:
> http://mail.okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> 


_______________________________________
http://www.okiebenz.com

To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://mail.okiebenz.com/mailman/listinfo/mercedes_okiebenz.com

Reply via email to